I am about to add a couple of spurs to a ring that is not RCD protected. The neighbour definitely wants them channeled in rather than surface trunking so I have to RCD protect. It is an old Tenby CU with crabtree SB6000 MCB's. I have found a 32A RCCB which fits this board (see below)

Sb6000 rcbo 32a.jpg

The modern RCBO's are self explanatory with there flying neutral and (sometimes) earth and I am 99.9% certain this is right (diagram below) but I just wanted some reassurance that I take a single 2.5mm[SUP]2 [/SUP]conductor to neutral bar from N Supply, as the RCCB looks different to any of the modern ones.

RCCB.jpg
Thanks..
 
correct apart from the neutral link needs to be greater than 2.5mm?

Could you explain a little more please? The ring is on a 2.5mm, why would the supply neutral need to be bigger for the RCCB if its just dealing with that one circuit?
 
Think, think! It's an RFC.
If it were an MCB, how many 2.5s would be connected to it?
 