did a cu change on friday. tt system, simple split load board, dual rcds. Theres a fault on one of the lighting circuits. when one of the light switches is turned on it trips out BOTH rcds on the CU.
going back to the house shortly to further investigate. would this be a borrowed neutral on...
robsparx
Thread
borrowed
landing
light
lighting
neutral
out
rcd
rcds
tripping
on changing fuse boards has anyone got a sucssesful method of testing for borrowed neutrals before changing ?
finding probs on changing boards then to find borrowed neutrals on two way lighting on stairs and wall lights
thanks for any feedback !
I seem to be having alot of trouble after installing anew consumer unit with 5 RCBO's I have got really high milli second readings and dont understand why I am looking at 350 x 1 and no operation on x 5. IR is fine and so is R1 + R2. Any suggestions????:confused:
Sorry for this dumb question....
What would be the easiest way of testing to see if you have a borrowed neutral?
Disconnect neutrals in cu and do a continuity test between neutrals?:confused:
My apologies in advance....
i had a phone call off my mate today he had done cu change ,dual rcd as per 17th,he said alls fine until i turn on the landing light (2 way switch) and both the rcds keep tripping,turns out he had put up lights and down lights on different rcds as recomended,turns out when the council wired the...