went to domestic job today where max demand was 236A (around 175A after diversity) main fuse is 100A so demand seems high to me...just wondered when you design what demand do you go to
hi guys new to this so sorry if revisiting old stuff.
I need to run a sub main 200M from the service head to a log cabin
Super eco all LED etc, so 40A 9Kw max demand
if i use the cable calculators i get 185mm cable
we all know power networks cover huge distance with 35mm cable on 100A supply...
belliezzz
Thread
building
cable
demand
main
outbuilding
sub main
supply
unless
voltage
looking to get a bit of help got a job that currently has 8 flats and a landlord supply and a big office on the ground and basement
After using the OSG for diversity have come up with the following
118A per flat (no gas)
127A for landlord (lift etc)
180A for office (air con)...
daveb1
Thread
3 phase
access
demand
flats
kva
maximum
office
phase
supply
Hi all, I appreciate this has probably being posted time and time again, but I'm using my phone and the search threads button isn't working.
Basically I'm just starting my design course (2396) project and I'm on with working out the max demand and diversity, basically I've split the job up and...
For SSE DNO area, if a customer was to request an upgrade of supply from 60A to 80A (or 100A), does anyone know if SSE normally make a charge for doing this?
Background: TN-S supply (Ze = 0.27 Ohm), late 1960's Bakelite-looking head which appears in good condition, mixture of 16 and 25mm2...
Hi guys, I'm looking to install a sub board to feed 4x 8.5kw shower circuits and 2x 2 ring 3kw hob circuits (4x32amp MCB's and 2x16amp MCB's). What would be the best method to work out the maximum demand? I get 83amps. Many thanks in advance.
Hi, i require a little advice. 3 phase supply (100A per phase) from energy meter into 3 phase switched fuse isolator, then swa off to D.B 20 metres away. Distribution board feeds office equipment only. I need to install a supply for a 36kw 3p machine, which is going to be situated next to...
In preparation of wiring up a commercial premises (function rooms / bars / restaurant area) I am trying to determine to what extent the existing 60A single phase supply might need upgrading. I have not had to do this myself for a commercial premises, and I am wondering if the same rules apply as...
Currently completing 2396 project (cant wait to see the back of it!!) Would just like to check im on the right wavelength when calculating max demand and diversity
DB1 Maximum Demand & Diversity
Lighting - 90% of total demand.
Total demand of lighting circuits is 50.48amps. After...
Hi all
There is a commercial complex that I am inspecting, testing and certificating, and doing any necessary remedial work. I have now got my client's insurance company demanding my credentials regarding being NICEIC registered (I am registered with one of the others), and that I have to prove...
kkkkk
Thread
anything
being
company
demand
insurance
proof
prove
registered
Wonder if I can get some guidance, on max demand in block of flats. It always was hard for me as it always comes to massive demands, and I red here that it all comes with years of experience and that it is like an art. This is first bigger project I am taking on. So please don’t shoot.
I need...
Hi guys I'm after a bit of help with working out my Max Demand normally in a domestic situation its fine but theres so many heaters and water heaters on this that I'm a bit confused.
I have been asked to do a bit of commercial installation for a kitchen and toilets its a children's soft play...
Is there a voltage drop from DNO transformer to incoming supply? For a standard 100A supply to a house so they design cable to with stand no VD as so at maximum demand there will be no VD. It is then up to us to design circuits as to have as little as possible so that 230v remains everywhere. Of...
Hi all,
sorry to bring this up again but I cant quite find the answer I need for an assessment
As part of a rewire the ground floor has 20 double 13amp sockets but 9 of these are in the kitchen.
I have been told the kitchen is drawing sockets will have:
13.3 amps from a washer dryer
13.3 amps...
Can someone help me work out a max demand
got a
40amp shower
32 amp cooker
16 amp radial
16 amp radial
32 amp ring
6 amp lighting
6 amp lighting
whats the calculation to work out max demand please
Hi,
I am looking for a little advise on how to apply diversity and work out maximum demand on a new installation I am designing in a Cabin.
Cabin CU has 3 circuits
Circuit 1
6 Socket outlets - to supply 2.7KW Floor standing Hair dryer
Electric Oil filled radiator
Hand held hair dryer
Kettle...
hi guys. if i calculate maximum demand like i got 6 circuit
32a cooker
32a upstairs ring
32a down s. ring
20a,radial
6a upstairs light
6a down stairs light get the higgest one and add the rest together get 40% of it and finally add to highest one.. do u thing is that right??
and also do...