went to domestic job today where max demand was 236A (around 175A after diversity) main fuse is 100A so demand seems high to me...just wondered when you design what demand do you go to
Original question was how much do u go to
Not that helpful
Original question was how much do u go to
To the size of the incoming fuse!
Not that helpful
Neither is your info. What's in the garage that is drawing 50A ?
Anything nice growing in the garage?
Not that helpful
How do u clamp..at design stage..would b intersing to see that being done :O
50 amp supply from main to board to board in garage with 32 a ring ...6a lights...6a outside lights .....16a hot tub.....20a outside socket ...I know it wont use any near but thats what the design is..I didnt design it I just interested in design opinions
Or how many extension leads are plugged in
Can't be bothered reading all the previous posts but DNO's allow 2KW per average domestic dwelling. That's not even 9 amps.
Here's a example for you
If a 32 amp radial had 2 single sockets on it, and another 32 amp radial has 12 single sockets on it which one is the bigger load?
this must have been done ..what....a thousand times eng....you can keep on till your blue in the face about Max. demand & diversity....Maybe looking over the ''Similar Threads'' at the bottom of this page (All marked up with ''Max Demand'' as the title, or part of the title) will at the very least educate you a little, as to how you would go about initially assessing the max demand of an existing installation....