Hi all,
I've tested several radial circuits and only getting 0.00 ohms on the r+r2 test (zero'd leads)
2 of the radials only supplies one socket each and are approx. 3 metres in total length. (zs 0.25 and 0.21)
Another radial only supplies one socket and is appox. 5m in length. (zs 0.35)
The...
Has anyone experienced issues with continuity readings fluctuating on a Megger 1730 MFT when the test leads rotate/move in the instrument as is the unavoidable condition when actually using the tester?
I can null the leads but thereafter the reading with the leads connected to each other can...
Sting Ray
Thread
continuity
instrument
issue
leads
megger
megger mft
mft
readings
using
I think I have a faulty 66kva transformer but have little to no experience with them (delta star I believe)
Call out due to reported problems from some of the tenants (offices that are rented within part of the building)
some RCD protected ring final circuits disconnecting. Investigated at the...
Danspark
Thread
earth
fault
faulty
neutral
readings
transformer
voltage
I'm doing an continuity test on a lighting circuit and I'm getting funny readings I'm putting on test lead on earth and one on switch live then I'm getting a reading of around 1.4 ohms but then when I'm checking the polarity it's shooting up to around 93 ohms but not breaking the circuit as you...
So I'm doing a job and when connecting up a wall light to a single 1.5mm T+E it does not work, there is another wall light that is connected up to another single T+E cable, however this 9one does work.
when testing the cable coming out of the wall when connected into a connector block with no...
Tested each of 9 new circuits in usual way of L.O.C. and IR, all in theory ok ... CCU is a Hagar split-load dual RCD. 1-4 on RCD1 / 5 - 9 on RCD2
Aware that no requirement for "collective" IR on EIC, just individual circuits.
When tested from the outgoing L of the RCD2 to MCB busbar (all...
Hi everybody,
I have encountered a problem with EFL (Zs) testing a couple of times recently.
I have had unusually high readings for the length of circuit and earthing system type and the increase in impedance seems to be coming from resistance across the line pole of the RCD in the consumer...
Hi guys
A little advice here would be much appreciated , it's been a long head ache day!
Had a ring circuit in a house today with high readings end to end on all three , they where in there 40s , 50s and 60s but got a good r1 + r2 and a good Zs , is this normal to be able to have high end to...
nc12345
Thread
cables
check
circuit
readings
sockets
three
values
Does anyone else have problems with there continuity readings my readings never seem to be stable for example a newly installed ring end to end resistance on neutral and line ill get .46 and then a reading of .04 on line end to end the leads are always nulled and I even check readings on calcard...
A measured test shows a reading of 0.00 ohms. I have always when got this reading recorded it as 0.00 ohms on any test results sheet. As I have always believed it is a reading and must be recorded as such, I have also seen it written somewhere in either the NiCEiC Inspection and Testing Book or...
I recently bought a megger 1730 and i`m getting some weird earth loop readings using the no trip function. I know they can be a little higher at times when taking a "no trip" reading as my old 1552 was always a little higher too but these seemed well out...
I only got the meter this week (Used...
Just landed a new job. It's only been 4 days and I'm about to quit today. The role involves working on gas meters (wall testing).
They want me to manually take readings from 20 gas meters on a wall. Each meter has about 15 data information which i need to type into a tablet held by my left...
monjoor
Thread
electrical work
electronics
job
meters
new
readings
software
Hi there, Have been carrying out testing on some 3 phase sub-DB's that have outgoing supplies to 3-phase DB's for accommodation blocks. My problem is to do with readings I'm getting on a ground fault relay which has been set to 300mA. Basically, the incoming cable to the Sub DB ( 4-core 25mm...
Went to look at wiring a biomass boiler today ...
boiler and buffer tank located in a breeze block out building sat on concrete pad .
PME earthing system , existing supply to outbuilding in 25mm 3core swa .
ALL the pipework was in place (copper and steel pipe) connecting buffer tank and...
Hi all I keep having problems with my fluke the continuity readings are all over the shop never stable I always check my readings on a calcard before testing and when nulled I get correct reading i will test it on calcard 5 minutes later and it's half an ohm out so never know if I am getting an...
Lilyrose08
Thread
continuity
fluke
leads
problem
readings
socket
switch
Hello I've recently been called to a job regarding high earth fault loop readings through out the house they've got an old style mk consumer unit with a 30ma 60a main switch mk LN5760 the supply side of the rcd had good readings and but the load side readings were more than double that of the...
Was at a property toady which I've done previous work before including fuseboard change. All i did today was change a few socket plates over for new ones. Took some Zs readings and noticed they were very near the limit of being acceptable ie: 0.92, 0.98 etc.
Took a Ze at the board with main...
OK peeps
I have just tested an 185 4 core SWA, and have got readings of 40 Megs on L2 to earth and L3 to earth. Although this is accepatable according to the regs, I feel it is unacceptable as a NEW installation, and indeed there is evidence of water on some of the switchgear, which clearly...
Guest 004
Thread
acceptable
cable
cores
installation
new
readings
switchgear
water
I havent come across this before, wondered if its common and what it signifies in the ring.
Remeasured 3 times and got within 20mohms or so each time so pretty sure its not a zeroing the meter thing.
2.5:1.5 TW/E ring. I went around all of downstairs rooms, did min of few sockets in each room...
SpannerSpark
Thread
approx
around
friday
pretty
r1+r2
readings
ring
socket
sockets
I am part way through a condition report for a customer.
The house is generally in good condition but the electrical installation is quite old.
Although the rings are properly installed as ring final circuits, the 2.5 mm t and e cable is stranded and the Cpc appears to be 1 mm rather than 1.5...