You're right, Im confusing myself on this thread! If its not fused down (13A) then the 1.5mm (L/N) is generally non-compliant and should ideally be 2.5mm.
I say "generally" as although the cable should be matched to the OPD if its a single 13A socket and the method of installation/factors etc .. allows the cable to carry more than 13A the regs permit its installation. (I wont open the can of worms as there are other threads around where this is discussed pros/cons!).
Hi all, thanks for the replies. There were two double sockets flush mounted wired in 1.5/1mm T+E, from a existing 2.5/1.5mm 32A ring socket point!- no fusing at any point!! only had the kettle, toaster and microwave plugged in! I told the client that it was quite dangerous and would advise remedial work or if not then I would have to note it on the certificate and issue a warning notice of the defect. To my shock he wanted it sorted so now has been rectified by bringing the ring down from the loft in 2.5/1.5mm, behind wall cupboards and then trunking underneath with 2" drops to flush box's all looks very neat and only 1 tile damaged in the process! Thanks again and no doubt be posting again!