Can someone sanity check my thinking please....
An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with 60 amp fuse in it.
16 sq mm from cut out into a MET. Gas and Water bonding connected to the MET.
16 sq mm main earth from MET to the fused isolator.
Then 10 sq mm T+E glanded to the fused isolator and running off to a CU some distance away, cable route unknown and undiscoverable.
This means 4 sq mm CPC for this dist circuit. Let's assume the CPC meets the adiabatic equation.
My doubt's are:
1) Is there any nuance of PME earthing requirements that I've forgotten that renders this non-compliant? (noting the bonding is connected upstream).
2) I can't prove the 10 sq mm T+E is capable of carrying 60 amps as that would only apply if clipped direct and I can't verify the cable route
3) Similarly I can't prove if it requires RCD protection to cover impact protection or not, if it did it would also lead to selectivity issues.
Specific questions
1) This isn't an EICR, but if it was would you LIM this or assume the best and C3 it?
2) Would you be happy to move the fused isolator and extend the T+E by 3 meters and mechanically protect it to where a new service head is going. Or would you dig heels in an say a new SWA dist circuit is needed.
Many thanks!
An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with 60 amp fuse in it.
16 sq mm from cut out into a MET. Gas and Water bonding connected to the MET.
16 sq mm main earth from MET to the fused isolator.
Then 10 sq mm T+E glanded to the fused isolator and running off to a CU some distance away, cable route unknown and undiscoverable.
This means 4 sq mm CPC for this dist circuit. Let's assume the CPC meets the adiabatic equation.
My doubt's are:
1) Is there any nuance of PME earthing requirements that I've forgotten that renders this non-compliant? (noting the bonding is connected upstream).
2) I can't prove the 10 sq mm T+E is capable of carrying 60 amps as that would only apply if clipped direct and I can't verify the cable route
3) Similarly I can't prove if it requires RCD protection to cover impact protection or not, if it did it would also lead to selectivity issues.
Specific questions
1) This isn't an EICR, but if it was would you LIM this or assume the best and C3 it?
2) Would you be happy to move the fused isolator and extend the T+E by 3 meters and mechanically protect it to where a new service head is going. Or would you dig heels in an say a new SWA dist circuit is needed.
Many thanks!