AndyBuzz
OOps - Buzzlightyear - you answered my question !!
you can get a pair of xray glasses from amazon if that helps.how do you guys as sparks find out what fuse is actually fitted
Thanks again for replies.
I've just looked up looped supply and now understand the concept.
Do SSE have accurate records of whether I am on a looped supply, and the supply cable size(s) ? 35 years ago !!
We are very rural, in one of a pair of cottages fed from overhead. The overhead runs about 400 yards to a more substantial set of overheads. I remember 35 years ago the linesman who installed our supply saying there is a 400 amp switch box there for isolating our overhead.
I think this might be expensive - or I just abandon it all and forget the EV charging 'future proofing'. Keep to petrol !!
I'll contact them tomorrow - maybe they will do a survey.
I'd have preferred my electrician to do this but he's ill at the mo.
Thanks all for your support and replies. Though I'm not an electrician I can understand all your replies and what the fundemental issues are.
The better EV charges have a current transformer for the main supply and will adapt the charging to keep your total below 60A (assuming the house is below 60 of course!)Now I think I'm buggered. Can't run all that with 60 amp main fuse ?
A couple of recent customers have told me they have been contacted by their suppler to book in fitting a smart meter only to be told they can't have one as they have off peak which isn't supported. The whole system is a joke.I’m surprised they didn’t fit a smart meter. I thought all suppliers were pushing for them.
I take it that’s because of rural setting and maybe bad mobile signal for the smart communications.
We've also seen more than one example of this forum of smart meter installers not understanding off peak metering and having a go anyway, resulting in RCD's tripping every night...A couple of recent customers have told me they have been contacted by their suppler to book in fitting a smart meter only to be told they can't have one as they have off peak which isn't supported. The whole system is a joke.
Thanks pc1966The better EV charges have a current transformer for the main supply and will adapt the charging to keep your total below 60A (assuming the house is below 60 of course!)
So if charging and you put on an electric shower it just throttles the car charge for 10 minutes or whatever you are using it for.
Bigger issue is if you plan lots of electric heating or a massive range-style cooker, though I think some of the fancy induction ones also have total demand throttling (or am I imagining that?)
Yes - the installer said that as it's economy 7.A couple of recent customers have told me they have been contacted by their suppler to book in fitting a smart meter only to be told they can't have one as they have off peak which isn't supported. The whole system is a joke.
When you apply for an EV charge point, you have to request permission from your supplier, it's a standard form which is available here https://www.energynetworks.org/assets/images/Resource library/Single-Electric-Vehicle-Charge-Point-and-Heat-Pump-Installation-Application-Form.docThanks again for replies.
I've just looked up looped supply and now understand the concept.
Do SSE have accurate records of whether I am on a looped supply, and the supply cable size(s) ? 35 years ago !!
We are very rural, in one of a pair of cottages fed from overhead. The overhead runs about 400 yards to a more substantial set of overheads. I remember 35 years ago the linesman who installed our supply saying there is a 400 amp switch box there for isolating our overhead.
I think this might be expensive - or I just abandon it all and forget the EV charging 'future proofing'. Keep to petrol !!
I'll contact them tomorrow - maybe they will do a survey.
I'd have preferred my electrician to do this but he's ill at the mo.
Thanks all for your support and replies. Though I'm not an electrician I can understand all your replies and what the fundemental issues are.
With all the regs changes covering even what sparks can have for lunch, I'm surprised that correct labelling of the main fuse isn't mandetory within regs. At work if we supplied any equipment everything HAD to be correctly labelled. Seems a bit odd to me that the DNO can have a blasé approach just because it's their fuse.That’s the funny thing;
Our test certificates asks us to fill in a box what size the main fuse is…. But we are not allowed to pull it to find out
we have to go by the sticker on the fuse carrier… which in experience … is either “100A” or “60/80” which still doesn’t help… which is it? 60 or 80?
The carrier is moulded with 100A printed into the plastic, as others have said, that’s the rating of the carrier- the biggest fuse that can go in.
I’m surprised they didn’t fit a smart meter. I thought all suppliers were pushing for them.
I take it that’s because of rural setting and maybe bad mobile signal for the smart communications.
Thanks for the detail and esp the form link.When you apply for an EV charge point, you have to request permission from your supplier, it's a standard form which is available here https://www.energynetworks.org/assets/images/Resource library/Single-Electric-Vehicle-Charge-Point-and-Heat-Pump-Installation-Application-Form.doc
They then check their network diagrams, loadings etc before you can connect an EV charge point.
You can submit one yourself any time so consider putting one through and you will get your answer without any commitment on your part.
Note it's the same form if you want to install heat pumps as well.
Note, the fuse carrier states 100A as this is the maximum, just like a standard plug says 13A - you could have a 3A, 5A.... etc fuse installed.
One point is to look at the meter, it usually has a maximum of 80A, so that's a clear indication you wouldn't have a 100A fuse!
Can the op not use the off-peak for the car charging then?

Hello Andy.When you apply for an EV charge point, you have to request permission from your supplier, it's a standard form which is available here https://www.energynetworks.org/assets/images/Resource library/Single-Electric-Vehicle-Charge-Point-and-Heat-Pump-Installation-Application-Form.doc
They then check their network diagrams, loadings etc before you can connect an EV charge point.
You can submit one yourself any time so consider putting one through and you will get your answer without any commitment on your part.
Note it's the same form if you want to install heat pumps as well.
Note, the fuse carrier states 100A as this is the maximum, just like a standard plug says 13A - you could have a 3A, 5A.... etc fuse installed.
One point is to look at the meter, it usually has a maximum of 80A, so that's a clear indication you wouldn't have a 100A fuse!