Sly

Hi Gents

Client requirement is for 125 kVA Distribution Board,
What does it mean ?

Thanks
 
A db capable of supplying 125kva? So kw = kva x pf. I'd guess that they want a db capable of roughly 250a
 
amps when KW is known (3 phase calc shown). 125kva is 100KW

kW x 1000
1.73 x E x PF

E is the voltage(400) and PF around 0.8

I get 180A per phase max

Amps where KVA is known

kVA x 1000
1.73 x E

Or single phase

kVA x 1000
E

=543A.

Correct me if I'm wrong
 
It’s 180A at 400V.

But now I’m going to ask a serious question. Are you competent to undertake this?


To ask the question in the first place would suggest not. I’m sorry but it’s not aunties fuse board under the stairs.
 
I just had a look in the mirror and it really does say mug on my forehead.
Nice one Sly, you got me
Now go get a life:)
 
Slipped up ther lads!!!!!!


I'm as bad as the B&Q man giving advice in the electrical isle.

Concerned how he gets the work.....
 