How would everyone feel about a 240Y system in a building with everything connected Line-Line?

I personally like (want) this system. No TN-C, TN-C-S vs TN-S debate. No earthing/bonding debates of how to keep the neutrals separate in a multi source or generator system. No fire or shock risk from a broken PEN/MEN. No need to keep track of live and neutral in a circuit.

Just asking curious.
 
This was quite common in mainland Europe at one time but AFAIK never used in the UK. It requires double-pole fusing and switching for single-phase loads, which we do not generally adopt, and reduces the overall system voltage by sqrt(3) meaning more copper is needed for the same power. If you are not going to use the neutral then there's no real point distributing that, so you might as well call it a delta supply. Ground a centre-tap on one winding and you've got the US system, which is ingenious and versatile but through UK eyes, when we're used to working with 400V, the amount of current you need to do anything useful seems terribly cumbersome.

You seem to be trying to solve a problem that doesn't exist. If you don't accept the risk of a MEN / CNE, then make it TN-S and use 5 wires everywhere. You'll still use less copper than lowering the line-line voltage to 240V and getting rid of the neutral.
 
But there is a point in distributing it (as a PE) in an effort to create a low impedance path to facilitate the operation of over current devices.

TN-S still has the risk of open neutral.

But I will agree with you, the copper will be greater. Perhaps double is not more in some cases.
 
Sure, running single-phase loads line-line eliminates the possibility of damage by overvoltage from a broken neutral. I've seen plenty of that in my line of work. But in TN-S the impact is an economic one, not one of shock protection. Which is cheaper, replacing stuff broken by overvoltage or running heavier cables? There is a possible incidental benefit of imposing double-pole OCPD and switching on things out of necessity, although that could be introduced in regulations even for 1P+N+E.

The case for / against PME on grounds of shock risk is separate.
 
Because you would still have a dangerously high potential to earth at the lamp fitting.

So mr.homeowner could inadvertently touch something lethal changing a blown lamp.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Earth

Thread Information

Title
138/240Y System
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
Cookie,
Last reply from
Cookie,
Replies
18
Views
2,604

Advert

Back
Top