Ok so i might get ripped to shreds for this but here go's. Been to look at a job this morning, customer wants to move a couple of switches from a wall theyre having knocked down and have an additional socket installed. Carried out a couple of checks, gas and water bond ok, tns supply which enters the property in the garage, and here is where my concern lies. The supply to the DB is in 16mm2 t&e. Fed via a 80a kmf switch. The cable is clipped surface in the garage and then disappears into the ceiling void within the house. There is no RCD protection for this cable. Fitting any 30ma device upstream to protect it isnt really an option as the DB is split load with one side unprotected and one side having 80a 30ma RCD protection, leaving me with no discrimination. I then thought of using a 100ma time delayed RCD but realised this would not achieve the required disconnection time. In an ideal wolrd this t&e cable would be replaced for a swa but this just isnt practical as the house is immaculate and theres no way the customer will pay for this. Ive told them i'll ask a few questions and do a bit of reading before i start any work. I was thinking could it be argued that the t&e cable supplying the DB isnt actually concealed in any walls, as it is clipped direct in the garage before it disapears into the ceiling void, only to then enter the DB which is mounted right underneath the ceiling?
 
you've answered part of your query. the 16mm does not require RCD, unless required for ADS. e.g. a TT earthing system. more to the point is whether the cpc in the 16mm is adequate to carry the PEFC.
 
and if you have PME earthing and that cpc is also a main bonding conductor, then 10mm is the min. size.
 
16mm2 t&e supply

All main bonding conductors are 10mm2 and come back to an earth bar at the meter position. Doesnt look like any bonding conductors come from the MET in the DB
 
OK, so that rules out that one. do the adiabatic for the cpc after measuring the pefc.
 

Reply to 16mm2 t&e supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
511
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
855
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock