Discuss 18th Regulation 411.3.4 in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Afternoon all,


Have a quotation regarding garage lighting which requires alteration. It’s a set of flats with a seperate large garage area which id class as commercial hence not needing an rcd as reg Regulation 411.3.4 states only in domestic.
The head of the flats is saying it’s classed as domestic area.
Board is mcbs but unsure I’ll squeeze a RCBO. C


Can you also just cover your own alterations with RCD or does it now have to be at the origin? I’d read on this forum it’s changed


Thanks in advance
 
Regulation 411.3.4 has no mention of installation method anyway?!

It doesn't have to, as far as I know (Don't own a BBB) it just means all lighting circuits in a domestic property must have additional protection, regardless of installation method.

If outside of a domestic environment an you had T&E buried in a wall less than 50mm it would need the additional protection because of a different regulation.
 
Thanks guys for your input.

If a alteration takes place on a lighting circuit do you need to cover the whole circuit by means of RCD protection or just your additional works?
 
Thats how I read it and as it’s clipped direct I’m just trying to determine if it’s a commercial area.

Is it being used for commercial purposes, is it solely occupied by businesses who pay business rates etc etc.
Or is it a bunch of domestic garages belonging to domestic properties/ intended for use in association with domestic properties?
 
I'd bet if you looked at the tenancy agreement for the flats, commercial use of the garages is specificaly prohibited.

That will be why the head of the flats is saying it’s classed as a Domestic area
 
Why pick over the difference of interpretation, seems it very likely to be domestic, just rcd protect the circuit with an independent rcd or rcd FCU above the board if you can

Then rest easy!

If in doubt just do worst case then you should not be caught out

Unless the cost is prohibitive that is, which in this case it seems trivial
 

Reply to 18th Regulation 411.3.4 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening all. I have a question as I can’t get my head around something with solar PV I’m going to be working on a new build in a couple of...
Replies
9
Views
2K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
607
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Short Version Is it permissible to have 2 feeds to 2 separate consumer units in a detached garage? Is it permissible to run SWA underground...
Replies
15
Views
3K
Hi I’m looking for advice on the following: I’ve yet to contact my local council about installing a light in Zone 1 of my bathroom (this due to...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock