This is not really a grey area.
BS7671 gives us table 41.5 - Maximum earth fault loop impedance (Zs) for RCDs. This is for TT systems.
For an RCD with a rated residual operating current of 30mA, the maximum earth fault loop impedance (Zs) is given as 1667 ohms. We are referred to note 2 below, which states that a value exceeding 200 ohms may not be stable.
It would therefore not be unreasonable to use this figure of 200 ohms in the Max Zs column on the EIC. It would also not be wrong to state the maximum value given in table 41.5, ie 1667 ohms, because that's what's written in black and white.
If we were to use the Max Zs tables for MCBs to BS60898 and put down the figure of 1.37 ohms or the 1.1 ohms corrected figure, and we enter the measured value of Zs for the circuit as (for example) 27.5 ohms, we would be effectively certifying that this particular circuit does NOT comply with the required disconnection time.
Also, as has already been stated by others, the Max Zs column is applicable only to an earth fault, not a short circuit from Line to Neutral.
@Julie. makes a good case for considering the effective disconnection of the circuit by the MCB in the case of a line to neutral fault in a TT system, in relation to what would in fact be the L-N fault loop impedance. As far as I'm aware, BS7671 does not give any tables for L-N fault loop impedance. However, the charts giving the time/current characteristics for MCBs can be consulted for this purpose.