What would you put-in the EIC column for Max Loop reading permitted for a TT system, for a 32 amp 60898.
Protected by Rcd 30ma,Dual split DB.
Protected by Rcd 30ma,Dual split DB.
Yea I thought that , but been told to enter 200 ohms,relevant for the Max on TT System.1667 as it's using a 30mA RCD for fault protection.
Agree its a bit of a grey area. The Max Loop Impedance (Zs) refers to the Line-Earth Loop so should be a big clue!grey area .
Agree, & this becomes a problem, the 3.9 reading refers to line & earth not L & N,I’ve done loads of calculations for this scenario,& it’s a worry,when circuits on TN System are not complying to the Zs required, & a rcbo is then used.The operating curve/required time to operate is the same for the mcb aspect irrespective of if the fault is L-N or L-E/CPC.
In this case then, with a measured value of circ 3.79 ohm, which could be around 4.44 ohm when running hot, we could have a fault current (@95% of voltage - the minimum allowed) of 230 x 0.95 / 4.44 = 49A or so.
For a standard 32A mcb this represents a trip time around 200 seconds - close to 3 1/2 mins!
Even at full voltage, and a cold cable, it's still several mins before it trips.
Does this sound OK?
Agree, & this becomes a problem, the 3.9 reading refers to line & earth not L & N,I’ve done loads of calculations for this scenario,& it’s a worry,when circuits on TN System are not complying to the Zs required, & a rcbo is then used.
No is the answer to your question,sorry.
Yep....it seems more in theses times with the younger generation,just fit a Rcd/rcbo not thinking of the implicactions involved.Off to work have a good day.Agree, we are furiously agreeing with each other.
It depends on how the Zs is made up, if the r1 is 0.5 ohm, r2 = 0.83 ohm, and Ze =
2.46 ohm (but Z1 [line-neutral] = 0.1 ohm)
Then although the Zs (earth fault) would be 3.79; recalculating for r1+rn +Z1 = 1.1 ohm - which is just about ok.
Made up figures here of course.
But completely agree with your worries, I think the same, it's unfortunate that the process, which is a shortcut very suitable for TNx systems is applied to TT, it completely misses out valuable checks.
I really don't like substituting a proper design by "just add a rcd - that will clear it" type logic, in my mind the design should try to achieve everything properly and only rely on rcds as a last resort.
Unfortunately this view isn't shared by all, with so many just relying on a single rcd to perform magic!
Correct, there isn't a requirement to operate for L-N or L-L faults within any set time but 434.x does say that protection against fault current is required, to me that does mean it has to operate in a timely manner, not necessary 0.2/0.4 sec - or even 5 sec but not several mins.Meeting disconnection times comes under chapter 41 - Protection against electric shock, which I don't think would be a concern for L-N faults (or perhaps it might be, on a TN-C-S?). So to disconnect in <= 0.2s for L-N fault on TT is not necessary.
There are of course other considerations - adiabatic and cable rating.
Not very convincing, I don't think anyone has answered the OP original question!Does this sound OK?
If its not so 'grey' it should be pretty obvious!What would you put-in the EIC column for Max Loop reading permitted for a TT system, for a 32 amp 60898.
Protected by Rcd 30ma,Dual split DB.