Okay so I'm just finishing up an EICR for a tenanted property. The property has been looked after and the ecletrical installation is excellent condition considering its age of around 50-60 years. There have been no alterations other than a new DB completed by others around 5 years ago.
I have a 2.5/1.0 ring final supplying all sockets in the two bed flat including the kitchen.
my end to ends were as follows:
r1 0.41Ω
rn 0.41Ω
r2 0.99Ω
Max Zs measured was 0.8Ω at a spur, all other points measured around 0.58-0.60Ω
Lowest IR reading was across L-E which measured 252 MΩ
The circuit is on a 32A BSEN61009 RCBO.
Realistically this installation has operated perfectly for the last 5 decades and common sense tells me it's fine; however, my quandary...
When using the lowest Zs the adiabatic tells me that this the CPC is undersized, but when using the highest Zs a 1.0mm2 CPC is perfectly adequate.
So my question(s):
1. Which Zs value would you use for the adiabatic equation?
2. Would you C3 the 1.0mm2 CPC or C2 it, especially if the equation tells you that the CPC is undersized?
Would love to hear how you'd handle this.
I have a 2.5/1.0 ring final supplying all sockets in the two bed flat including the kitchen.
my end to ends were as follows:
r1 0.41Ω
rn 0.41Ω
r2 0.99Ω
Max Zs measured was 0.8Ω at a spur, all other points measured around 0.58-0.60Ω
Lowest IR reading was across L-E which measured 252 MΩ
The circuit is on a 32A BSEN61009 RCBO.
Realistically this installation has operated perfectly for the last 5 decades and common sense tells me it's fine; however, my quandary...
When using the lowest Zs the adiabatic tells me that this the CPC is undersized, but when using the highest Zs a 1.0mm2 CPC is perfectly adequate.
So my question(s):
1. Which Zs value would you use for the adiabatic equation?
2. Would you C3 the 1.0mm2 CPC or C2 it, especially if the equation tells you that the CPC is undersized?
Would love to hear how you'd handle this.