cliffed
What would you put-in the EIC column for Max Loop reading permitted for a TT system, for a 32 amp 60898.
Protected by Rcd 30ma,Dual split DB.
From memory it would be 1.37 x 0.8 = 1.1 ohm, assuming type B, half that for type C half again for type D.
Measured values should be in the osg.
grey area . when we consider fault protection, generally it's a fault (short) from a live part to an exposed conductive (earthed ) part. in which case, the RCD is performing the role of fault protection, and Zs is the resistance of the earth fault path. when we come to L-N shorts, the MCB will operate irrespective of the Zs and high Ze due to TT. bear in mind that the ELFI relates to L-E faults, not L-N.
We need to check everything will be safe and disconnect in all conditions, under normal circumstances, the r1+r2 is slightly larger than r1+rn due to smaller cpc, so if the mcb works and disconnects for r1+r2 it will do so for r1+rn.
However, in the TT case, the r1+r2 is so much bigger than r1+rn that we have to provide specialist protection to cater for it - the rcd. But the previous assumption that if the mcb will operate for earth faults, it will also operate for line-neutral faults just isn't the case here, therefore we must confirm it is ok.
So check of loop to ensure mcb operation for line-neutral faults, and check of rcd operation for faults including earth.
Hence why we must check the loop against the mcb - using a valid mcb max loop impedance (which if close, you could legitimately use r1+rn) and the rcd by confirmation that it operates via actually testing it. (The cross check via comparing resistance values is basically because we can't actually test the mcb)
grey area .
Agree its a bit of a grey area. The Max Loop Impedance (Zs) refers to the Line-Earth Loop so should be a big clue!
Some lines of thought are that it should be the maximum for the RCD (50/0.03) =1667ohms.
Some, the maximum for MCB at 0.2secs disconnection time even though its unlikely to meet that requirement if TT.
Never thought to enter 200hms!
BS7671 suggests 200 ohm for earth electrode resistance and anything above this may be unstable. Why you should enter this on a schedule is odd as it is external and does not include the circuit impedance.
This is not really a grey area.
BS7671 gives us table 41.5 - Maximum earth fault loop impedance (Zs) for RCDs. This is for TT systems.
For an RCD with a rated residual operating current of 30mA, the maximum earth fault loop impedance (Zs) is given as 1667 ohms. We are referred to note 2 below, which states that a value exceeding 200 ohms may not be stable.
It would therefore not be unreasonable to use this figure of 200 ohms in the Max Zs column on the EIC. It would also not be wrong to state the maximum value given in table 41.5, ie 1667 ohms, because that's what's written in black and white.
If we were to use the Max Zs tables for MCBs to BS60898 and put down the figure of 1.37 ohms or the 1.1 ohms corrected figure, and we enter the measured value of Zs for the circuit as (for example) 27.5 ohms, we would be effectively certifying that this particular circuit does NOT comply with the required disconnection time.
Also, as has already been stated by others, the Max Zs column is applicable only to an earth fault, not a short circuit from Line to Neutral.
@Julie. makes a good case for considering the effective disconnection of the circuit by the MCB in the case of a line to neutral fault in a TT system, in relation to what would in fact be the L-N fault loop impedance. As far as I'm aware, BS7671 does not give any tables for L-N fault loop impedance. However, the charts giving the time/current characteristics for MCBs can be consulted for this purpose.
The operating curve/required time to operate is the same for the mcb aspect irrespective of if the fault is L-N or L-E/CPC.
In this case then, with a measured value of circ 3.79 ohm, which could be around 4.44 ohm when running hot, we could have a fault current (@95% of voltage - the minimum allowed) of 230 x 0.95 / 4.44 = 49A or so.
For a standard 32A mcb this represents a trip time around 200 seconds - close to 3 1/2 mins!
Even at full voltage, and a cold cable, it's still several mins before it trips.
Does this sound OK?
Does this sound OK?
Agree, & this becomes a problem, the 3.9 reading refers to line & earth not L & N,I’ve done loads of calculations for this scenario,& it’s a worry,when circuits on TN System are not complying to the Zs required, & a rcbo is then used.
No is the answer to your question,sorry.
Agree, we are furiously agreeing with each other.
It depends on how the Zs is made up, if the r1 is 0.5 ohm, r2 = 0.83 ohm, and Ze =
2.46 ohm (but Z1 [line-neutral] = 0.1 ohm)
Then although the Zs (earth fault) would be 3.79; recalculating for r1+rn +Z1 = 1.1 ohm - which is just about ok.
Made up figures here of course.
But completely agree with your worries, I think the same, it's unfortunate that the process, which is a shortcut very suitable for TNx systems is applied to TT, it completely misses out valuable checks.
I really don't like substituting a proper design by "just add a rcd - that will clear it" type logic, in my mind the design should try to achieve everything properly and only rely on rcds as a last resort.
Unfortunately this view isn't shared by all, with so many just relying on a single rcd to perform magic!
Yep....it seems more in theses times with the younger generation,just fit a Rcd/rcbo not thinking of the implicactions involved.Off to work have a good day.