Hi there. I know that in theory the IR test on a lighting cct requires all loads to be removed (ideally), and the 2 way switching operated and several readings taken - to ensure both strappers are tested. My question is on the logic behind the multiple readings. When the light being controlled by 2/3 way switches is ON, then in theory both strappers, plus the common are live - for a L/E IR test nothing has been missed. So once the lamps are disconnected prior to the actual test - I'm guessing it is assumed you will not know the state of the cct (would the light be ON if plugged in?) hence two tests with one of the 2/3 way switches being flicked inbetween - doesn't matter which? Is this correct. Just curious....Obviously for a 3 way lighting cct there are 8 combinations if you wanted to going running up and down the stairs all day..and if you had 2 sets of 3 way lighting on the same cct....
 
Okay - bit of a blond moment. Of course forgot the other method of wiring 2/3 way - which does leave floating strappers when the light is on. Please ignore
 
It's good to see you figured it out. Using the old grey matter is the best way to retain such info!
 