been digging around to try to avoid this post - in case I'm making a fool of myself again - but here goes anyway. Just like IR tests am I right in thinking the Zs value needs to be obtained with the 2/3 way switches in their different positions? Otherwise how do you find a high impedance issue in one of the strappers that takes Zs too high - and which might not be tested depending on the switch positions? Cheers
 
Although I can test I'd not class myself as particularly clued up on all the ins and out... But I think you may have a valid point, although I only test light circuits at the furthest point (wait for the screams of outrage). It would surely only show up if the 2way circuit was part of the switching of that lighting point.
 
Although I can test I'd not class myself as particularly clued up on all the ins and out... But I think you may have a valid point, although I only test light circuits at the furthest point (wait for the screams of outrage). It would surely only show up if the 2way circuit was part of the switching of that lighting point.

Yes - only affects bulb controlled by 2/3 way switches. Occupant reaches up to change bulb on landing, dodgy metal fitting on the edge of live/earth fault, act of changing bulb causes fault to occur, while in contact. If say one of the L2 screws in the 2W switch has a medium/high impedance then 0.4s is not achieved. SO, strapper passes IR test, but not tested for good Zs value in one of the 2 way switch positions (COMMON?) plus dodgy metal light fitting (NOT RARE?) leads to dangerous condition.
 
Assuming all your IR and continuity tests are good, Zs at the furthest point should be good regardless of switch positions.
 
Assuming all your IR and continuity tests are good, Zs at the furthest point should be good regardless of switch positions.
Yes - but when occupant is hanging off a live pendant - they probably don't care what Zs at the furthest point is :) The issue here is not R2 continuity, but R1 - in particular the R1 strapper that doesn't get tested when Zs is measured AT this pendent - so AT this pendent there will be two Zs depending on whether the 'good' R1 strapper is in cct, OR the 'bad' R1 strapper is in cct.??
 
Assuming all your IR and continuity tests are good, Zs at the furthest point should be good regardless of switch positions.

and obviously a good Zs at the furthest point tells you your cable size and length are good - but doesn't tell you about any faults in earlier legs off
 
Yes - but when occupant is hanging off a live pendant - they probably don't care what Zs at the furthest point is :) The issue here is not R2 continuity, but R1 - in particular the R1 strapper that doesn't get tested when Zs is measured AT this pendent - so AT this pendent there will be two Zs depending on whether the 'good' R1 strapper is in cct, OR the 'bad' R1 strapper is in cct.??

Red bit...well they're dead, so sod it!

Assuming you're using 3 core, all your measurements will be the same, therefore equal Z esses!
You'll pick up any dodgy connections doing your dead continuity tests.

If you're getting different live readings (and the cct is good) they'll be from crappy probe contact and instrument error.
If your measurements are within required max Zs, seriously, don't worry about it!
 
Red bit...well they're dead, so sod it!

Assuming you're using 3 core, all your measurements will be the same, therefore equal Z esses!
You'll pick up any dodgy connections doing your dead continuity tests.

If you're getting different live readings (and the cct is good) they'll be from crappy probe contact and instrument error.
If your measurements are within required max Zs, seriously, don't worry about it!

Thanks for the reply again. Obviously the R1+R2 continuity check would also pick up the problem IF this test was carried out with both strappers i.e. 2 tests with the switches flicked over inbetween. Is this what you mean?
 
You only need to test twice, both switches in their on or off positions.

I'm going to make you Lofty's apprentice if you're not careful! :-)
 
You only need to test twice, both switches in their on or off positions.

I'm going to make you Lofty's apprentice if you're not careful! :-)
Okay, my point is still essentially the same though. The OSG Testing section details the continuity tests, IR tests, and Zs tests. It is only in the IR tests that 2 way lighting is mentioned, with the need to perform more than one test with the switches in different positions. SO.... to put my original question slightly differently..."when doing the R1+R2 test, surely the 2 way lighting needs multiple tests"
 
Yes, you have to do as many tests to confirm the validity of all the cables there maybe in a circuit.
Remember, the OSG is just a guide to the regs.
Get yourself GN3, covers I&T in much more depth.
 
Yes, you have to do as many tests to confirm the validity of all the cables there maybe in a circuit.
Remember, the OSG is just a guide to the regs.
Get yourself GN3, covers I&T in much more depth.
Thanks Archy - yes I should shell out a bit more on a more comprehensive book - cheers for your help. In your reply - both switches to off, then both to on - I presume if an intermediate switch is also present this stays untouched throughout??
 