Installed two PIRS today operating one 30w LED security light. Wired 2 feeds to each sensor , then both switch wires connected to live on the security light , neutrals joined straight through.

When the timer cuts out on sensor and lights goes off , it starts strobing slightly , not on full power just very faint.

Only happens with two sensors wired one sensor works perfectly normal. Only suggestion I have is a back feed coming through one of the PIRs ? No neutral fault.

Jamie
 
ok think its solid state , and from reading online could be voltage leakage through PIR. Is there anything I can do to this ? will adding more load help ?

Jamie
 
Probably won't help. Solid state switches often leak, with incandescant lamps it's not enough to cause a noticable problem but with LED's it's enough to charge some of the capacitors on the input side of the driver which then discharge suddenly periodically causing flickering/flashing strobe type effect you mentioned.

I'd suggest replace the PIR's with relay output types and have done with it. You can add some electronic components to combat the issue with the existing setup but it's usually more trouble than it's worth.
 
Probably won't help. Solid state switches often leak, with incandescant lamps it's not enough to cause a noticable problem but with LED's it's enough to charge some of the capacitors on the input side of the driver which then discharge suddenly periodically causing flickering/flashing strobe type effect you mentioned.

I'd suggest replace the PIR's with relay output types and have done with it. You can add some electronic components to combat the issue with the existing setup but it's usually more trouble than it's worth.


Thanks Marvo , Any idea why both PIRs are working ok when used on there own ? Leaking voltage/flickering only happens when both PIRs connected ?

The way its connected , If PIR 1 makes , it will also send the switched live to the other PIR. Is it perhaps that voltage is being fed into PIR 2 , from PIR 1 , rather than from the actually PIR in PIR 2 ? If tat makes sense ! its like voltage fed in backwards to PIR 2 . Rather than PIR 2 sensing movement and the switchwire becoming live , the switch wire is being made live with out the PIR being activate ?

confusing ...Id rather not add more PIRs if I can. Instead I may be better just adding a second light as both are in relatively same area
 
The way you are joining the two PIRs is a very uncommon way because mainly it would have been joined in a serial manner but considering your depiction I was unable to understand why the problem is arising when the second PIR is connected because in generally if it is working fine when connected individually then it should also work in same way when connected to one another. IMO just remove the PIR and go with the usual method.