Hi all, im new the the forum.

Curently doing the city and guilds 2365 level 3 course. Got a question regarding the 305 design assignment.

When filling out the table to calculate the voltage drop and calbles sizes, do i use the design current etc before or after the diversity factor?

15587068790904772971554881245015.jpg
 
Design current (Ib) is the acceptable current after diversity has been taken into account
An example might be:
12kW cooker total current flowing if all elements were on simultaneously = 12000/218.5 (worst case) = 54.9A.
That would require a 10mm2 cable
Apply diversity owing to rheostats switching in and out and we have (54.9 - 10)*30% +10 + 5 (if appropriate) = 23.47A
You might get away with a 2.5mm2 cable .

To become an electrician you have to do this stuff for yourself .......
 
I only recall ever applying diversity to things like cookers, or anything above 13a devices. Never for rings, radials or lighting circuits.

We went over and over this stuff until it sunk in long enough to pass the module and it only came up in a few questions when we finally sat the test.

Apart from electrical science where you really need to apply physics based maths it was all study your notes for X module, take test, pass test.
 
In question 4 its to do with cable calculations so you select the right csa & protective device, fault current etc.

Question 6 if I remember correctly asks you to show loads before & after diversity is applied so you can calculate max demand etc.
 
I haven't seen the latest set of practical papers. but from memory they were very basic and simplified.

Diversity comes into its own when designing large electrical installations where the designer has to take into consideration the loading in large complex systems where there maybe 20 to 30 ring final circuits besides a selection of more basic radials such as condensers, heating and HVAC systems.
C&G uses the OSG which covers the very basic circuits and loading which are applicable to circuits protected by up to 100A service fuses. at 16kA maximum
 

Reply to 2365 305 design question in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi I'm currently doing C&G 2365 Level 3 I'm working through the 305 design assignment (Swimming pool, hotel etc.) Other then this assignment I...
Replies
4
Views
4K
Hi All! I'm starting my level 3 course soon and have been going through my course notes and textbook doing the cable calcs etc. But i want to get...
Replies
4
Views
2K
I have a run of conduit 172ft from a 12x12 box which branches out to parking equipment with runs about 50ft from the box. My voltage drop calc...
Replies
0
Views
2K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock