S
shambock
Hi
Anyone help with some cable calcs for my designe project, i must be missing something here.
Im trying to work out and show my calculations for cable sizing of a 32A ring
Length is 78 M
Number of 13A double sockets is 7
Ib is 32A
In is 32A RCBO
It should be In / Correction factors of wich i only have a grouping factor of 0.41
This makes it 32/0.41 = 78A
The above formula say that i should be using a cable capable of carrying 78A wich brings it upto 25mm ????????????? (ref meth B,singles) table 4D1A.
I know this is wrong but where am i mucking up.
Please help
Personally I would use Ib of 26A for a ring final circuit.
As for sizing cable, BS 7671 stipulates that it must have a current carrying capacity of at least 20 amperes.
Upvote 0
YOUR NUMBERS sound ok, just checked the BRB. Perhaps I am wrong! Is this just a question to check for your understanding of the regs etc.. with maybe the next part 'ok, so this is obviously Unpractical, so how would you design the installation differently'?
Upvote 0
Didn't know if you were given the figure in an example or had worked it out - possibly incorrectly.
Are there no variables?
Upvote 0
No this is my deign from scratch
Upvote 0
OK Voltz hope you have better luck than me.
Length is 78 M run in trunking and conduit - ref meth B (probably singles)
Ib is 32A
In is 32A RCBO
It - should be In / Correction factors of wich i only have a grouping factor of 0.41 for 16 circuits in trunking
if i get rid of correction factor i can get away with a 4mm cable
Good luck
Upvote 0
Luck ran out. I await words from the wise ones! I have personally run many, many time, circuits in 4"x4" trunking (ok maybe not up to 16, but maybe) in schools, hospitals etc..
Standard lighting and power in 2.5mm, 1.5mm, singles, and it has all been designed, inspected, and passed. There is something definitely amiss here. How on earth do you propose to terminate said conductors at accessories?
I too have followed the cable calculations protocol and come out with the same results. What do they design large capacity trunking for?
Lets hope we find out the answer. I feel a naked lady coming on!
Upvote 0
I'm not sure what you are trying to do exactly but you will have to change the derating factor by choosing another installation method.
Are the circuits all 78m run together? Move the db or have an additional one nearer.
Upvote 0
is that not for just checking expected values of R1 + R2 on a RFC test? or is there something else about design I missed?
Upvote 0
Ring circuit cable tabulated rating (It) formula
In BS7671 the rules are changed for the special case of the 30 and 32 A final ring circuit (Regulation 433.1.5), where overload protection requirements are amended allowing 20 A rated cables (Iz > or equal to 20 A) providing the load current in any part of the ring is unlikely to exceed 20 A.
Therefore Iz > or equal to 20 but Iz = It Ca Cg Ci Cc
Hence It > or equal to 20/(CaCgCiCc)
Example
A ring final circuit wired in thermoplastic (PVC) cable a sper Table 4D5 enclosed in conduit in an insulated wall and protected by a 32 A circuit breaker (In = 32 A); the cable rating must equal or exceed 20 A. The cable rating,
It > or equal to 20/(CaCgCiCc) if Ca = Cg = Ci = Cc = 1 then It > or equal to 20 A
From Table 4D5 (column 7) a 2.5mm cable is therefore adequate.
Upvote 0