H
Hogshaw
Hey folks
sitting 2394 written exam tomorrow and have a few questions in my notes I need the textbook answers for.
1. State four practical steps that the inspector can take during the inspection and test process to ensure the safety of the users of the building, other than safe isolation.
2. State what would be verified when confirming that additional protection has been provided using RCD's
any references would be helpful
cheers guys
Place barriers
Place obstacles
Erect warning notices
Give audible warnings to the users of the premise
Cables are installed at a depth of less than 50mm and are not mechanically protected
RCD is <30ma for additional protection
For number 2 see 415.1.1 and 612.13.1 and GN3 2.7.18 for a full explanation. Remember, verification includes testing.
The RCD needs to be tested to verify it does not exceed the required operating times.
It is all in GN3 :smile:
1. rusty nails has given the stock answer., and gets all 4 marks.:coolgleamA:
2. That the Earth Fault loop impedance for the circuit/s is compliant, The RCD is 30mA, and trips within 40 mS at 150mA (5 times I delta N)on both half cycles. The mechanical test button functions properly.
GN3 will elaborate where i haven't.
Cheers................Howard