Checked the SQ-D mcb tech' section, if you have a 16A (D) then the max is 4 * 400w metal halides.
All the mcb brands usually sing a similar tune, making this a type (c) or (b), increasing the no' of lamps or decreasing the mcb rating will all make you prone to nuisance tripping on start up.Note using to type (d) will limit your allowable ELI dramatically so take this into account when running long runs.
 
Checked the SQ-D mcb tech' section, if you have a 16A (D) then the max is 4 * 400w metal halides.
All the mcb brands usually sing a similar tune, making this a type (c) or (b), increasing the no' of lamps or decreasing the mcb rating will all make you prone to nuisance tripping on start up.Note using to type (d) will limit your allowable ELI dramatically so take this into account when running long runs.

so 8 x 250 W on a 20 should be about the max, Still don't fancy all that conduit work
 
so 8 x 250 W on a 20 should be about the max, Still don't fancy all that conduit work
It doesnt calculate like that its what the mcb's inrush can withstand with multiple inductives loads and this doesn't calculate uniformly thats why you need to pick your method then refer to the tech on your brand of mcb.
Ive followed so many sparkies who think 1.8 factor applies when working out mcb rating and type on inductive loads and this is not the case, then they scratch their heads when the get a call about mcb's tripping when lights switched on.
College dont touch on this subject and i believe they should. Well they didnt in my days.
 