Hi all,

Can anyone help me as to how to calculate the maximum demand on a 3 ph supply for cable sizing?

Can i just quickly estimate the demand by the breakers and multiply by a g factor i got from the IET design guide for sparks. eg 250 amps counting the breakers x 0.7 factor for mixed process mills


Thanks in advanced
 
Hi Kev.

For initial design brief this would be ok.

I would though be careful when using this estimation method as you need to be sure on the type of loading you will have at your dis board i.e inductive/resistive, aswell as the amount.

For your paper mill I would use the 0.7 factor also, to air on the side of safety.

Obviously when all info is available then a more detailed max demand calc should be done.

Cheers.
 
cheers lenny,

Another quick one is it correct that i divide by sqrt of 3 to find the demand per phase ie 250amp x 0.7 =175 then 175amp divided by sqrt of 3 =101amp?


Thanks in again
 
Hey Kev.

Unless you've got a purely balanced 3phase load then that isn't going to be very accurate.

It's almost impossible to get each phase at exactly the same loading, if you had any single phase loads for instance.

Cheers
 
Hi again

The thing is Lenny ive gone into this job today and counted the breakers and come up with 250amp say and multiplied it by the 0.7 factor and got say 175 amp only on one of the boards and another spark has come in after ive gone and said there is only 75 amp per phase so a 35mm supply cable will do for both boards:confused:. ive already ordered the 70mm armoured i think is right its just proving to the client why i think 70mm. so do i just go off the 175amp i got and add it to the 2nd board and then sqrt to get an overall load? or dont i even have to use the sqrt?

:confused:confused
 
Hi Kev.

I would use the total load of 175A for board 1.
For board 2 can you do the same, total all circuits and multiply by 0.7 again.

Add these two for the total load of both boards and you should be covered for whatever the situation then.

Cheers.
 

Reply to 3 ph cable calculations in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock