Hi Guys need a bit of expert advice and guidance. I have been asked to do a bit of work at my friends new office premises. The office is located inside a warehouse and is Fed via a 16 Way 3 Phase Distribution board with a 35mm 4-Core SWA.

However the Dist board is almost full and even after stripping out some old supplies that are not required I will not have enough room for some of the new circuits that are required. This is where I require help, Is it possible for me to either

A. Run a set of tails from one of the 3 Phases in the Main switch with a Neutral and Earth and install a single phase Consumer unit..... or

B. Run a set of tails from all 3 phases with a Neutral and Earth and install another smaller 3 phase Dist board.

Bearing in mind the Mains powering the 16Way Dist board already installed comes from a load centre at the far end of the warehouse.

I hope this all makes sense and look forward to your guidance and advice, Thanks in advance.
 
Hi Paul there is a Ring main for a Kitchen area complete with a fridge, washing machine, dishwasher, and waste disposal unit. There is also a Hob being installed was going to put it on its own supply, an undersink water heater, There are 2 more ring mains for 14 sockets for Computers etc, possibly 3 smal electric fan heaters (overdoor)and 2 handryers (optional)
 
install a single phase unit, move smaller loads (lights, alarm etc) in there, should give you more space on the 3 phase board.
do an estimate of the loads and split them between 3 available phases not to cause imbalance.
 
What do you suggest I do then Dave?

Without seeing the installation or knowing a lot more about the installation I can't really suggest much.
What is the submain fused at?
What is the existing average and maximum demand on this submain? Is this measured or calculated?
Does it have the capacity to feed your new circuits?
What would be the consequences of a fault on one of the new circuits taking out all of the new circuits?
Can the new circuits be spread over three phases or would they be better all on the same phase?
What impact will the new circuits have on the phase balance if they do go on one phase only?
Does the existing submain have a reduced csa neutral? Will your new circuits have an effect on this of it does?
 
Another option not mentioned depending on load/capacity etc is to move existing circuits into a new board as above (amlu) and use the new spare way freed up by this to feed the sub board from an appropriately rated Mcb
 
Another option not mentioned depending on load/capacity etc is to move existing circuits into a new board as above (amlu) and use the new spare way freed up by this to feed the sub board from an appropriately rated Mcb

This would be poor design, feeding a submain of an mcb would render little to no disrimination between the possible 40 - 63amp OCPD and the circuits in the new board a nightmare if you lose all your computers because of a faulty element in a kettle on a different circuit.

You should not feed submains mcb boards off a front end mcb, especially in the OP's set-up.
 
Would it be preferable to 'upgrade' the 16 way board to one that can handle the new capacity required (load requirements withstanding)? It may be better to do it this way rather than increase capacity by adding on in other ways (no pun intended)!
 

Reply to 3 Phase dist board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
696
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
491
Hi Looking at a job currently adding a 3 phase solar installation but the distribution board is full obviously a new board is the best option but...
Replies
9
Views
1K
Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin...
Replies
5
Views
925
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
572

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock