P Pockets Feb 17, 2012 #1 Does anyone know the maximum Zs for a 35 Amp cartridge fuse? any info would be great and where you found it.
Does anyone know the maximum Zs for a 35 Amp cartridge fuse? any info would be great and where you found it.
telectrix ~ Mentor Arms Feb 17, 2012 #2 bs1361? bs88? by interpolating the time/current tables in bs7671, the current required for 0.4 sec. disconnection is approx. 220A. so max. Zs would be 230/220 = 1.045 ohms. nearest i can come up with. Last edited: Feb 17, 2012
bs1361? bs88? by interpolating the time/current tables in bs7671, the current required for 0.4 sec. disconnection is approx. 220A. so max. Zs would be 230/220 = 1.045 ohms. nearest i can come up with.