YOU SET THE MFT TO TYPE AC AND TEST 1X.....EVEN IF TYPE A.....EASY
To be completely fair I don’t think we’ve established beyond doubt that he didn’t do that.
I’d like to know which Robin tester was used and whether they are 30ma rcbos.
As this is all quite intriguing so I don’t want to scare the OP away either!
 
This could easily get confusing....

Before amendment 2 they were tested at X 1/2, X1 and X5
So a 30ma RCD would be tested at 15ma, 30ma and 150ma.
They were also tested on a rising and falling wave pattern (0 degrees and 180 degrees)
The pass results were no trip at 1/2, 300ms at x1 and 40ms at x5

(I had assumed you were talking about 350ms, hence my units comment, but let's forget that.)

Since amendment 2 the minimum testing is reduced to testing at x1, so just 30ma.

Now your 2nd comment about brand new Hager Type A's not tripping until you give them 300ma is interesting.
It would be exceptional for 9 to all fail by such a margin, so I can only conclude the tester is setup wrong, the tester is faulty, there is something strange with the installation or (respectfully) you are making a mistake somehow.

A barrage of questions follow.....!
Is the main earth at the CU connected?
What exact tester are you using?
What does the RCBO say on it for I delta N, post a photo if you have one.
Are you setting it to type AC?
Have you tried testing at the output terminals with no load?
Have you already done IR testing and did you do it with the RCBO's in situ?

You can nearly detect 300ms without a tester; when you press the test button do you get an instant snappy trip or a trip after about 1/3 second.

I'll stop now....and hope someone can figure this one ou

To be completely fair I don’t think we’ve established beyond doubt that he didn’t do that.
I’d like to know which Robin tester was used and whether they are 30ma rcbos.
As this is all quite intriguing so I don’t want to scare the OP away either!
The installation is in a s/s food servery unit and is only about 3m long,so no long circuits and no loads to affect the
rcbos.Gone online and hager do,nt appear to make a rcbo above 30ma,or an s type rcbo.Will check again on Monday
and report back.The meter is a robin KMP 5404.Have just tested a wylex 32A A at home and it tests at 30ma no problem.
Regards,S
 
The meter is a robin KMP 5404
I can’t give you a technical reason why but I have heard of others having problems with that tester (which is rather antiquated to be honest) and RCBOs.
A google search pulls up some examples on the IET forum.
I strongly suspect the test instrument is the issue.
 
Last edited:
The installation is in a s/s food servery unit and is only about 3m long,so no long circuits and no loads to affect the
rcbos.Gone online and hager do,nt appear to make a rcbo above 30ma,or an s type rcbo.Will check again on Monday
and report back.The meter is a robin KMP 5404.Have just tested a wylex 32A A at home and it tests at 30ma no problem.
Regards,S

Your initial post & thread title stated RCD and I didn't spot the mention of RCBO when replying to your later post, hence commenting about the possibility of having received 300mA units.

While it wouldn't explain a trip current of 350mA, they certainly offer 100mA RCBOs.
 
my mft is so old.it's due for pension, but it still works and done a Zs on lno tripp where a robinn came up with error---noise.
 
my mft is so old.it's due for pension, but it still works and done a Zs on lno tripp where a robinn came up with error---noise.
I don’t have anything against separate testers, or old testers per se, but the old Robin Loop and RCD testers aren’t really very useful these days. Both don’t cope with RCBOs. (The loop tester is ok on the high current tests.)
I’ve known other RCD testers that draw their power from the circuit under test to do funny things with RCBOs, possibly due to inrush current.

That one doesn’t mention compatibility with 61009 devices in the manual.

If it were me I’d try the test button, as you can tell if it’s instant or 1/3rd of a second, and assuming they seem snappy I’d try another tester.
(Kt63 or 1553 are good 2nd hand buys)
 
I don’t have anything against separate testers, or old testers per se, but the old Robin Loop and RCD testers aren’t really very useful these days. Both don’t cope with RCBOs. (The loop tester is ok on the high current tests.)
I’ve known other RCD testers that draw their power from the circuit under test to do funny things with RCBOs, possibly due to inrush current.

That one doesn’t mention compatibility with 61009 devices in the manual.

If it were me I’d try the test button, as you can tell if it’s instant or 1/3rd of a second, and assuming they seem snappy I’d try another tester.
(Kt63 or 1553 are good 2nd hand buys)
mine is a 1553 bought 2nd hand from a forum member 11 years ago. does everything i need apart from making beer.
 

Reply to 350ma test for type A rcds in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
661
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
791
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
916

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock