Just wondered how we would know a 30ma type A rcd/rcbo will trip at 30ma,if we
can only test it at 350ma?Think I must be missing something.Thanks for any help.
Regards,S
 
Just wondered how we would know a 30ma type A rcd/rcbo will trip at 30ma,if we
can only test it at 350ma?Think I must be missing something.Thanks for any help.
Regards,S
As of AMD 2 of 7671:2018, the only test that is needed for any type RCDs is a simple test at the rated residual operating current.

So the test is now at 30mA, with a requirement that it disconnects within 300ms.

Previously, the test for an RCD offering additional protection was at 5x or 150mA (disconnecting within 40ms).

If the RCD was offering fault protection, then the 1x test was relevant (disconnection within 300ms - but to ensure the disconnection within 0.4 seconds required by fault protection), though in most cases both were tested using the auto RCD function on many testers.

The BS standard for RCBOs did allow an alternative of testing at 250mA to achieve the 40ms disconnection - the first type A Hager ones did that, which led to a lot of confusion with test meters that couldn't easily test at 250mA. They have since changed their design so they work as expected, though there are likely still some out there.

So going forward it's simpler - and even the earliest MFTs can be used to test any type of RCD.

Of course, its a minimum standard, so people can continue to do the additional tests.
 
It's been pointed out to me that the latest Guidance Note advises against testing as we previously did, simply to extend device life.
Another point is that the vast majority of new devices trip within 40ms anyway even when testing at x1.
It's a heck of a lot quicker going along at x1/2 and then at x1.
 
It's been pointed out to me that the latest Guidance Note advises against testing as we previously did, simply to extend device life.
Another point is that the vast majority of new devices trip within 40ms anyway even when testing at x1.
It's a heck of a lot quicker going along at x1/2 and then at x1.
Yes, note 6.
Since RCDs are only rated for a finite number of operations, carrying out frequent
optional tests can shorten the product’s life. For example, in carrying out all of the above tests, including optional tests, for a 30 mA Type B RCD, would require the RCD to trip 12 times.

Also says:

Where RCDs are installed with circuit-breakers and the circuit has the characteristics to satisfy Chapter 41 of BS 7671 without the RCD, then testing of the RCD is not essential unless it is specified for additional protection.​

So there's even an argument that for non socket/domestic luminaire circuits on TN-S/TN-C-S where cabling is not buried there is no need to test RCBOs at all other than the test button? Not sure what would be put in the schedule though - LIM? N/V?
 
Just wondered how we would know a 30ma type A rcd/rcbo will trip at 30ma,if we
can only test it at 350ma?Think I must be missing something.Thanks for any help.
Regards,S
You test it as a Type AC, dont change settings on mft....As from September only need to do test at 1x, unless carrying out an EICR when you need to do 1x and 5x
 
You test it as a Type AC, dont change settings on mft....As from September only need to do test at 1x, unless carrying out an EICR when you need to do 1x and 5x
It's only 1x on any form of testing, EICR or initial I believe. The 5x are additional optional tests according to GN3, for troubleshooting or diagnosis purposes only, not for routine testing and specifically not for compliance with BS7671.
 
So there's even an argument that for non socket/domestic luminaire circuits on TN-S/TN-C-S where cabling is not buried there is no need to test RCBOs at all other than the test button? Not sure what would be put in the schedule though - LIM? N/V?
Yeah, that bit is interesting.
To be honest I've been ignoring it. For EICR's I usually haven't got a clue how cables are run so I take the view that if they are they they need to be tested and work, and for IV it feels unprofessional to not ensure they actually work even if it isn't actually required.
 
Yeah, that bit is interesting.
To be honest I've been ignoring it. For EICR's I usually haven't got a clue how cables are run so I take the view that if they are they they need to be tested and work, and for IV it feels unprofessional to not ensure they actually work even if it isn't actually required.
I have my NICEIC assessment next Friday so I may bring this up - I always like to have some 'talking points' - stops them looking too closely at the paperwork 😉

I'm thinking of a case where there is a surface mounted cable that feeds a fixed appliance.

In future, we won't be able to test AFDDs other than the test button after all, and we don't test MCBs apart from functional switching.

Not sure what the rest of Europe or the world does with RCD testing? US seems to get by with very little testing, though of course they are different in many ways and not necessarily a guide to best practise.
 
It's only 1x on any form of testing, EICR or initial I believe. The 5x are additional optional tests according to GN3, for troubleshooting or diagnosis purposes only, not for routine testing and specifically not for compliance with BS7671.
Correct....just checked and my certs have not been upgraded to amendment 2
 
Yes, note 6.
Since RCDs are only rated for a finite number of operations, carrying out frequent
optional tests can shorten the product’s life. For example, in carrying out all of the above tests, including optional tests, for a 30 mA Type B RCD, would require the RCD to trip 12 times.
I would be very surprised if MFT testing had any real impact on RCD life.

I can see they probably are only going to last a dozen or so high-current disconnections so repeatedly closing them on to a fault situation and hoping it stays on is not a good idea!
 
Sorry thought they were tested at 350ma?

Tested 9 brand new Hager rcbos (type A) today and they only tripped when the Robin was set to 300ma.So they must be old stock?
S

Why would age be a factor? 30mA is 30mA, just as it was 100 years ago.

Are they 30mA or 300mA RCDs?

What is their part number?

What trip current is indicated on the front? Perhaps 0.3A
 
Sorry thought they were tested at 350ma?

Tested 9 brand new Hager rcbos (type A) today and they only tripped when the Robin was set to 300ma.So they must be old stock?
S
This could easily get confusing....

Before amendment 2 they were tested at X 1/2, X1 and X5
So a 30ma RCD would be tested at 15ma, 30ma and 150ma.
They were also tested on a rising and falling wave pattern (0 degrees and 180 degrees)
The pass results were no trip at 1/2, 300ms at x1 and 40ms at x5

(I had assumed you were talking about 350ms, hence my units comment, but let's forget that.)

Since amendment 2 the minimum testing is reduced to testing at x1, so just 30ma.

Now your 2nd comment about brand new Hager Type A's not tripping until you give them 300ma is interesting.
It would be exceptional for 9 to all fail by such a margin, so I can only conclude the tester is setup wrong, the tester is faulty, there is something strange with the installation or (respectfully) you are making a mistake somehow.

A barrage of questions follow.....!
Is the main earth at the CU connected?
What exact tester are you using?
What does the RCBO say on it for I delta N, post a photo if you have one.
Are you setting it to type AC?
Have you tried testing at the output terminals with no load?
Have you already done IR testing and did you do it with the RCBO's in situ?

You can nearly detect 300ms without a tester; when you press the test button do you get an instant snappy trip or a trip after about 1/3 second.

I'll stop now....and hope someone can figure this one out!
 
Last edited:
Tested 9 brand new Hager rcbos (type A) today and they only tripped when the Robin was set to 300ma.So they must be old stock?
S

So they failed the test? What did you do next?

I would have been double checking everything to make sure I hadn't made a mistake at that point.
 
YOU SET THE MFT TO TYPE AC AND TEST 1X.....EVEN IF TYPE A.....EASY
To be completely fair I don’t think we’ve established beyond doubt that he didn’t do that.
I’d like to know which Robin tester was used and whether they are 30ma rcbos.
As this is all quite intriguing so I don’t want to scare the OP away either!
 
This could easily get confusing....

Before amendment 2 they were tested at X 1/2, X1 and X5
So a 30ma RCD would be tested at 15ma, 30ma and 150ma.
They were also tested on a rising and falling wave pattern (0 degrees and 180 degrees)
The pass results were no trip at 1/2, 300ms at x1 and 40ms at x5

(I had assumed you were talking about 350ms, hence my units comment, but let's forget that.)

Since amendment 2 the minimum testing is reduced to testing at x1, so just 30ma.

Now your 2nd comment about brand new Hager Type A's not tripping until you give them 300ma is interesting.
It would be exceptional for 9 to all fail by such a margin, so I can only conclude the tester is setup wrong, the tester is faulty, there is something strange with the installation or (respectfully) you are making a mistake somehow.

A barrage of questions follow.....!
Is the main earth at the CU connected?
What exact tester are you using?
What does the RCBO say on it for I delta N, post a photo if you have one.
Are you setting it to type AC?
Have you tried testing at the output terminals with no load?
Have you already done IR testing and did you do it with the RCBO's in situ?

You can nearly detect 300ms without a tester; when you press the test button do you get an instant snappy trip or a trip after about 1/3 second.

I'll stop now....and hope someone can figure this one ou

To be completely fair I don’t think we’ve established beyond doubt that he didn’t do that.
I’d like to know which Robin tester was used and whether they are 30ma rcbos.
As this is all quite intriguing so I don’t want to scare the OP away either!
The installation is in a s/s food servery unit and is only about 3m long,so no long circuits and no loads to affect the
rcbos.Gone online and hager do,nt appear to make a rcbo above 30ma,or an s type rcbo.Will check again on Monday
and report back.The meter is a robin KMP 5404.Have just tested a wylex 32A A at home and it tests at 30ma no problem.
Regards,S
 
The meter is a robin KMP 5404
I can’t give you a technical reason why but I have heard of others having problems with that tester (which is rather antiquated to be honest) and RCBOs.
A google search pulls up some examples on the IET forum.
I strongly suspect the test instrument is the issue.
 
Last edited:
The installation is in a s/s food servery unit and is only about 3m long,so no long circuits and no loads to affect the
rcbos.Gone online and hager do,nt appear to make a rcbo above 30ma,or an s type rcbo.Will check again on Monday
and report back.The meter is a robin KMP 5404.Have just tested a wylex 32A A at home and it tests at 30ma no problem.
Regards,S

Your initial post & thread title stated RCD and I didn't spot the mention of RCBO when replying to your later post, hence commenting about the possibility of having received 300mA units.

While it wouldn't explain a trip current of 350mA, they certainly offer 100mA RCBOs.
 
my mft is so old.it's due for pension, but it still works and done a Zs on lno tripp where a robinn came up with error---noise.
 
my mft is so old.it's due for pension, but it still works and done a Zs on lno tripp where a robinn came up with error---noise.
I don’t have anything against separate testers, or old testers per se, but the old Robin Loop and RCD testers aren’t really very useful these days. Both don’t cope with RCBOs. (The loop tester is ok on the high current tests.)
I’ve known other RCD testers that draw their power from the circuit under test to do funny things with RCBOs, possibly due to inrush current.

That one doesn’t mention compatibility with 61009 devices in the manual.

If it were me I’d try the test button, as you can tell if it’s instant or 1/3rd of a second, and assuming they seem snappy I’d try another tester.
(Kt63 or 1553 are good 2nd hand buys)
 
I don’t have anything against separate testers, or old testers per se, but the old Robin Loop and RCD testers aren’t really very useful these days. Both don’t cope with RCBOs. (The loop tester is ok on the high current tests.)
I’ve known other RCD testers that draw their power from the circuit under test to do funny things with RCBOs, possibly due to inrush current.

That one doesn’t mention compatibility with 61009 devices in the manual.

If it were me I’d try the test button, as you can tell if it’s instant or 1/3rd of a second, and assuming they seem snappy I’d try another tester.
(Kt63 or 1553 are good 2nd hand buys)
mine is a 1553 bought 2nd hand from a forum member 11 years ago. does everything i need apart from making beer.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
shipley
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
R L ELECTRICAL

Thread Information

Title
350ma test for type A rcds
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27
Unsolved
--

Advert

Thread statistics

Created
sinewove,
Last reply from
telectrix,
Replies
27
Views
2,669

Advert

Back
Top