As of AMD 2 of 7671:2018, the only test that is needed for any type RCDs is a simple test at the rated residual operating current.Just wondered how we would know a 30ma type A rcd/rcbo will trip at 30ma,if we
can only test it at 350ma?Think I must be missing something.Thanks for any help.
Regards,S
Yes, note 6.It's been pointed out to me that the latest Guidance Note advises against testing as we previously did, simply to extend device life.
Another point is that the vast majority of new devices trip within 40ms anyway even when testing at x1.
It's a heck of a lot quicker going along at x1/2 and then at x1.
You test it as a Type AC, dont change settings on mft....As from September only need to do test at 1x, unless carrying out an EICR when you need to do 1x and 5xJust wondered how we would know a 30ma type A rcd/rcbo will trip at 30ma,if we
can only test it at 350ma?Think I must be missing something.Thanks for any help.
Regards,S
It's only 1x on any form of testing, EICR or initial I believe. The 5x are additional optional tests according to GN3, for troubleshooting or diagnosis purposes only, not for routine testing and specifically not for compliance with BS7671.You test it as a Type AC, dont change settings on mft....As from September only need to do test at 1x, unless carrying out an EICR when you need to do 1x and 5x
Yeah, that bit is interesting.So there's even an argument that for non socket/domestic luminaire circuits on TN-S/TN-C-S where cabling is not buried there is no need to test RCBOs at all other than the test button? Not sure what would be put in the schedule though - LIM? N/V?
I have my NICEIC assessment next Friday so I may bring this up - I always like to have some 'talking points' - stops them looking too closely at the paperworkYeah, that bit is interesting.
To be honest I've been ignoring it. For EICR's I usually haven't got a clue how cables are run so I take the view that if they are they they need to be tested and work, and for IV it feels unprofessional to not ensure they actually work even if it isn't actually required.
Just wondered how we would know a 30ma type A rcd/rcbo will trip at 30ma,if we
can only test it at 350ma?Think I must be missing something.Thanks for any help.
Regards,S
Thats what I do lol, good to see you back and on form Dave.You set your tester to 30mA and test it.
Thats what I do lol, good to see you back and on form Dave.![]()
Correct....just checked and my certs have not been upgraded to amendment 2It's only 1x on any form of testing, EICR or initial I believe. The 5x are additional optional tests according to GN3, for troubleshooting or diagnosis purposes only, not for routine testing and specifically not for compliance with BS7671.
I would be very surprised if MFT testing had any real impact on RCD life.Yes, note 6.
Since RCDs are only rated for a finite number of operations, carrying out frequentoptional tests can shorten the product’s life. For example, in carrying out all of the above tests, including optional tests, for a 30 mA Type B RCD, would require the RCD to trip 12 times.
Sorry thought they were tested at 350ma?You are confusing units I think?
Tested 9 brand new Hager rcbos (type A) today and they only tripped when the Robin was set to 300ma.So they must be old stock?You set your tester to 30mA and test it.
Sorry thought they were tested at 350ma?
Tested 9 brand new Hager rcbos (type A) today and they only tripped when the Robin was set to 300ma.So they must be old stock?
S
This could easily get confusing....Sorry thought they were tested at 350ma?
Tested 9 brand new Hager rcbos (type A) today and they only tripped when the Robin was set to 300ma.So they must be old stock?
S
Any 2nd opinion with someone else's MFT to rule out a test fault?Tested 9 brand new Hager rcbos (type A) today and they only tripped when the Robin was set to 300ma.So they must be old stock?
Tested 9 brand new Hager rcbos (type A) today and they only tripped when the Robin was set to 300ma.So they must be old stock?
S
To be completely fair I don’t think we’ve established beyond doubt that he didn’t do that.YOU SET THE MFT TO TYPE AC AND TEST 1X.....EVEN IF TYPE A.....EASY
This could easily get confusing....
Before amendment 2 they were tested at X 1/2, X1 and X5
So a 30ma RCD would be tested at 15ma, 30ma and 150ma.
They were also tested on a rising and falling wave pattern (0 degrees and 180 degrees)
The pass results were no trip at 1/2, 300ms at x1 and 40ms at x5
(I had assumed you were talking about 350ms, hence my units comment, but let's forget that.)
Since amendment 2 the minimum testing is reduced to testing at x1, so just 30ma.
Now your 2nd comment about brand new Hager Type A's not tripping until you give them 300ma is interesting.
It would be exceptional for 9 to all fail by such a margin, so I can only conclude the tester is setup wrong, the tester is faulty, there is something strange with the installation or (respectfully) you are making a mistake somehow.
A barrage of questions follow.....!
Is the main earth at the CU connected?
What exact tester are you using?
What does the RCBO say on it for I delta N, post a photo if you have one.
Are you setting it to type AC?
Have you tried testing at the output terminals with no load?
Have you already done IR testing and did you do it with the RCBO's in situ?
You can nearly detect 300ms without a tester; when you press the test button do you get an instant snappy trip or a trip after about 1/3 second.
I'll stop now....and hope someone can figure this one ou
The installation is in a s/s food servery unit and is only about 3m long,so no long circuits and no loads to affect theTo be completely fair I don’t think we’ve established beyond doubt that he didn’t do that.
I’d like to know which Robin tester was used and whether they are 30ma rcbos.
As this is all quite intriguing so I don’t want to scare the OP away either!
I can’t give you a technical reason why but I have heard of others having problems with that tester (which is rather antiquated to be honest) and RCBOs.The meter is a robin KMP 5404
The installation is in a s/s food servery unit and is only about 3m long,so no long circuits and no loads to affect the
rcbos.Gone online and hager do,nt appear to make a rcbo above 30ma,or an s type rcbo.Will check again on Monday
and report back.The meter is a robin KMP 5404.Have just tested a wylex 32A A at home and it tests at 30ma no problem.
Regards,S
I don’t have anything against separate testers, or old testers per se, but the old Robin Loop and RCD testers aren’t really very useful these days. Both don’t cope with RCBOs. (The loop tester is ok on the high current tests.)my mft is so old.it's due for pension, but it still works and done a Zs on lno tripp where a robinn came up with error---noise.
mine is a 1553 bought 2nd hand from a forum member 11 years ago. does everything i need apart from making beer.I don’t have anything against separate testers, or old testers per se, but the old Robin Loop and RCD testers aren’t really very useful these days. Both don’t cope with RCBOs. (The loop tester is ok on the high current tests.)
I’ve known other RCD testers that draw their power from the circuit under test to do funny things with RCBOs, possibly due to inrush current.
That one doesn’t mention compatibility with 61009 devices in the manual.
If it were me I’d try the test button, as you can tell if it’s instant or 1/3rd of a second, and assuming they seem snappy I’d try another tester.
(Kt63 or 1553 are good 2nd hand buys)