Hi we have a client who insists on using 3kw induction hobs on their projects. These hobs are used 8-10hours per day and come with a moulded plug top. Safe to say the socket outlets keep melting/burning out. First thought was to remove the plug top and wire via a 16amp commando and appropriate 16amp rcbo (These sockets are wired on their own dedicated radial one radial per socket.) However removing the plug top would invalidate the warranty. The appliance is wired with a 1.5mm rubber flex. Not sure what else we can do with this other than tell the client to buy induction hobs that comes with a 16amp commando in the first instant. What's your thoughts on this? Thanks in advance.
 
I'm sure that the fact the manufacturers fitting a plug not suitable for the appliance rating / use is more of an issue than cutting the plug off.
However as above, I doubt the hobs are commercially rated or rated for continous use.

I used to do commercial work including Kitchens etc.
Anything over 2kw would sooner rather than later melt the plug /socket.
Part of the problem is the plug being removed before the appliance is cleaned and getting contaminaed with grease or cleaning product.

And 16amp plugs / sockets will melt as well, you need to go bigger.
 
A combination I have used (years ago though) to handle 3kW load is a black MK safety plug and an unswitched metalclad MK 13A surface mount socket:

13 Amp MK Safety Plug - Charcoal | MK (646CHA) - https://www.tlc-direct.co.uk/Products/MK0646CHA.html

MK Metal Clad Plus Socket Outlet Unswitched Aluminium K848ALM - https://www.builderdepot.co.uk/mk-metal-clad-plus-socket-outlet-unswitched-aluminium-k848alm?gclid=CjwKCAiArOqOBhBmEiwAsgeLmUbYRmilPQYcrAxwV6UMQka02uxE-vbzsdfvewYJMBlJZltSEhEo7xoC5sAQAvD_BwE

MAke sure the socket terminals for L and N are 'filled' with copper - so Barrymore if necessary - to maximise the thermal conductivity and assist heat transfer away from the socket-plug combo along the feed cable. Note - a Black plug to aid radiation of heat. If possible have a small loop of feed cable in free air.

Might work for you.
 
A combination I have used (years ago though) to handle 3kW load is a black MK safety plug and an unswitched metalclad MK 13A surface mount socket:
Good though to keep the switch's heat away! Can add a 20A DP isolator switch next to it as needed for safety when cleaning, etc.

@Daz2007 do they need to be unplugged at all? If not then a FCU would allow isolation by switching off for any cleaning, etc, and less risk of pings getting dirty/corroded and overheating as a result.
 
I've had a look and can't see anywhere where it says do not cut the plug off. It is a commercial hob.


Email the manufacturer/retailor and ask them.

 
Good though to keep the switch's heat away! Can add a 20A DP isolator switch next to it as needed for safety when cleaning, etc.

@Daz2007 do they need to be unplugged at all? If not then a FCU would allow isolation by switching off for any cleaning, etc, and less risk of pings getting dirty/corroded and overheating as a result.
The other aspect is the metal socket surface and back box to act like a heat sink and radiator.
 
OP: One might consider using so-called 'audio grade' 13A plugs and sockets which have silver or gold coated pins - silver and gold being very good conductors of electricity - silver being the better. Just google....

One has to minimise Ohmic heating viz I2R at all interfaces...........in order to achieve reliable long term ampacity.

Ampacity - Wikipedia - https://en.wikipedia.org/wiki/Ampacity

Rated current begs the question .............
 
Of course I do not know if it does nor if anything else I have said earlier might satisfy the client. But the OP has a client who wants a certain thing to be, and if it was me wanting to keep his client satisfied - as the OP seems too - I might say to him I have done some research and we could try these things and if they prove successful then ........

I understand from the opening post this is a repeat customer for the OP whom he aims to please if at all he can.
 
Something's gone very wrong with the design of these things if we have to rely on faceplates and back boxes as heatsinks to use them at their rated current
Yes. It's not that long ago that 3 kw loads were pretty much standard in kitchens and utilities. And there were never any question marks attached to a 13 amp plugtops ability to handle it.
 
I’ve seen various pictures of burnt moulded plug tops, ones that can’t be messed around with and whose connections should be correctly terminated. Some have been the actual fuse and fuse carry, the cause.

Seems quality cannot be guaranteed.
 

Reply to 3kw appliance moulded plug top in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
783
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
951
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
937
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock