Discuss 3p Tpn converted to Sp in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Last edited:
In this case both the L & N of the supply are carrying all of the load, so design-wise it should have upstream OCPD that is rated for that cable (as I suspect the sum of downstream MCBs is way higher).
 
It may have DP isolation but not at that location.
 
The neutral will only require switchable isolation in say a dwelling. Commercially the neutral requires a link to disconnect it
 
For that board no it just links the three lines. I believe the new Eaton ones become a double pole switch which also switches the neutral.
I know that I would fit a DP main switch, never seen a single phase supply without one.
Its a EICR so it’s been in place for some time, classification code C3 maybe after reading all these messages ?
 
I know that I would fit a DP main switch, never seen a single phase supply without one.
Its a EICR so it’s been in place for some time, classification code C3 maybe after reading all these messages ?
Explain why it needs Coding.
 

Reply to 3p Tpn converted to Sp in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi I always thought installations were safe at the time of instalment etc, the Distribution Boards at my works were installed over ten years back...
Replies
7
Views
864
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi all, So my factory needs more power, currently 100A/3p (70KVA) => 400A/3p (200KVA) UKPN wont upgrade existing supply and are insisting on new...
Replies
1
Views
366
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
629
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock