Apart from being the ultimate rough git, is there any electrical reason why i cart take the supply to the top of SW fuse instead of the bottom? (Cable lenth/space issues)

I feel im missing something bloody obvious but i don't know what.

Cheers Joe.
 
Then you would have to change the fuses live.
Normally the supply comes in, is switched and then goes to the fuses, if you wire it to the top of the fuses then switching off the switch will leave all the fuses still live.
 
  • Like
Reactions: 2 people
It depends if you have room in the switchfuse enclosure to dress cables around the internal gubbings to the input terminal at the bottom. Doubtful in today's miniaturized world... lol!!
 
Then you would have to change the fuses live.
Normally the supply comes in, is switched and then goes to the fuses, if you wire it to the top of the fuses then switching off the switch will leave all the fuses still live.

Not really the fuse carriage is withdrawn from both sides or it should be
 
This is the classic is it a switched fuse or a fused switch conundrum.
A fused switch it doesn’t matter which way the supply is presented as the fuse travels with the switch blades.
A switched fuse, if the supply enters the top the fuse will be live when you withdraw it.
 
  • Like
Reactions: 1 person
I was having an argument with a guy (Who worked in electrical wholesaler) in a bar, he was saying that he knew more about electrics, because he knew the difference between a a switched fuse and fused switch. I have no idea who won the argument as i was **** faced, but i assume it was me.

I Was having a bad day on the previous post, I actually Tested it in the end to check (Rotary isolator type, as opposed to the fork) and it does/did withdraw both ends, but i actually thought about it long enough to solve the problem without being a rough arse (which i hate) - I assume its a fused switch.

On another note, I was on a job, and found a bit of switch gear that im assuming is a damn sight older then me (Wood?) another fused switch lol.

http://i.Upload the image directly to the thread.com/KPnpUzP.jpg




 
You can still buy this set-up and is still common although the one in the pic may be older than you its hard to say 'not knowing your age'
 
It was branded the english electric company, I had a google, apparently they where taken over by GEC in 1968 no idea if they kept using the badge mind
 
That’s an EE fused switch still made today by GEC as System4. They started as EE Fortress back in the early 50’s. Bloody good gear. They are made up to 3200A.
Never had one fail.

Trying to switch some of the larger units off could be fun if they hadn’t been operated for a while. A scaffold pole came in handy more than once.

Home - Scatco Europa Ltd.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
3ph 100amp sw fuse
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
SparkyJoe,
Last reply from
Darkwood,
Replies
9
Views
108

Advert