Hi all,
I recently bought a CNC router and dust collector and need to connect it to my 3x380v+N power source.
I want the CNC router connected to the under/over voltage protection and the motor also connected to the overload protection.
Can someone please check if I connect the machines as in my schematic it will all work.
Learned in school how to, but that was more than 30 years ago 😉
Thanks in advance.cnc router wiring.jpeg
 
It looks OK to me, electrically. Consider whether there is a need to fuse down the contactor coil circuit, often there is not.

You would need to satisfy yourself that any safety requirements for the operation of the machinery are met according to your local regulations. If the CNC machine and extractor are complete in themselves, that should not be difficult.
 
It looks OK to me, electrically. Consider whether there is a need to fuse down the contactor coil circuit, often there is not.

You would need to satisfy yourself that any safety requirements for the operation of the machinery are met according to your local regulations. If the CNC machine and extractor are complete in themselves, that should not be difficult.
Thanks a lot for your professional advice, yes you are right, I think installing a fuse in the contactor circuit is better. Small expense, more safe.
 

Reply to 3Phase Motor breaker - overload schematic in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
313
Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
617
I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently...
Replies
18
Views
992
Hi I got called out to a faulty star delta starter on an old Stenner band saw Monday (was getting stuck in star and blow fuses) - So I ordered a...
Replies
19
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock