Good lord above! Where did you learn your trade?
I served my apprenticeship at a little local domestic building company and still got taught SWA, steel conduit and trunking, MICC, cable tray and bodgeit conduit and trunking (plastic).
 
Nooo. Swa, sy, steel conduit, flexi conduit, plastic/steel trunking im ok with but conduit and unistrut, what i mean is how would you include both of these and at what point. Come on guys, sorry if i sound abit thick, i proberly am mind you, just a little explanation pleaseeee
 
I see, makes sense now.
Use unistrut to bridge the gap and fix the conduit to it.

Unistrut is just a time saving way of building your own metal supporting structures and bracketry.
 
Oooo i see now thanyou dave. Sorry if i sounded thick, i keep doing that (not explaining myself properly). I never attempt anything im unsure of but thought it only got to come 2 mtrs off the wall and wanted to see the best ways others do it. Like i say i was just thinking tray off the wall across, 90 degree bend down the arm of the ramp to the controls on the ramp but werent sure if it would be sturdy enough. The unistrut that uve said sounds the best system thoe. Thankyou guys
 
Its hard to put what's in your head down in writing sometimes, I face exactly the same trouble so don't worry about that.

Personally I find tray to be a bit pointless when only putting one cable on it and there is never likely to be a need to add more down it. You'll find light duty tray to be as flimsy as bog roll, but the medium duty stuff far more rigid
 
You can even run the cable down the unistrut, but we went todo it one day to bridge between two outbuildings and the suit guy said no no no and made us Bolt two Pieces of uni strut to walls and put cable tray on top for 2 legs of fp. But that's the joy of government work, money no issue
 
Oooo i see now thanyou dave. Sorry if i sounded thick, i keep doing that (not explaining myself properly). I never attempt anything im unsure of but thought it only got to come 2 mtrs off the wall and wanted to see the best ways others do it. Like i say i was just thinking tray off the wall across, 90 degree bend down the arm of the ramp to the controls on the ramp but werent sure if it would be sturdy enough. The unistrut that uve said sounds the best system thoe. Thankyou guys
 
Uni strut across at high level, conduit drop to ramp fixed to unistrut at 90deg.at the top with a saddle.
Change from conduit to kopex at top of conduit (swan neck/angle box or whatever) and run it along the uni strut.
At the wall, change back to conduit and continue to isolator.
All assuming uni strut mounting is possible and secure.
 
Why the change to kopex along the unistrut?

I'd run conduit along the unistrut and a kopex drop to the ramp then down the side of the ramp in conduit depending on where connection box is. Kopex merely being there to take up any vibration or movement in the ramp.
 
I can see the ideas coming wrt tube, & kopex, however you'd still be running 6491 which is not suitable for connection to vibrating machinery anyway...

Mind neither is SWA, hence my thinking of possibly SY protected by Unistrut.
 
Is there much vibration of a lift??? Is there a deciding factor on when to use sy flex from data or do you have to judge yourself...
 
Guys, i cant thankyou all enough, ill be back there for an afternoon next week to talk through with the manager, so ill get some pics for you all. Literally thoe the whole workshop, the cable system is just cable ties and clipped direct if its not sagging cables. Is there a thanks button on this iphone app or is it just on the computer
 
Im not to sure about vibration, personally id say there couldnt be much at all, as its lifting a few tonne in the air
 