B bathroomboy Feb 15, 2009 #1 Have I read this right, just swotting up for my 2382 and looking at max disconnection times, the big red book Iv'e just spent £60 on says 0.2 in table 41.1 page 46, checked osg and it's what it should be 0.4
Have I read this right, just swotting up for my 2382 and looking at max disconnection times, the big red book Iv'e just spent £60 on says 0.2 in table 41.1 page 46, checked osg and it's what it should be 0.4
B bcm_spark Feb 15, 2009 #2 0.2s for TT me thinks, hence the need for an RCD. 0.4s for TN systems. Scrap that I just had a look in the book. Over 230v it is 0.2 seconds. Over 400v it is 0.1s Last edited by a moderator: Feb 15, 2009
0.2s for TT me thinks, hence the need for an RCD. 0.4s for TN systems. Scrap that I just had a look in the book. Over 230v it is 0.2 seconds. Over 400v it is 0.1s
S Spudnik Feb 17, 2009 #5 I think what you may be missing here is the OSG states 'not more than'. I must admit, the OSG does have a fair few errors in it and so now, i check 7671 just to make sure. Personally, i would go with the BRB rather than the OSG.
I think what you may be missing here is the OSG states 'not more than'. I must admit, the OSG does have a fair few errors in it and so now, i check 7671 just to make sure. Personally, i would go with the BRB rather than the OSG.