it is only for a few computers ......
Perhaps you should put it on a 16A mcb then if all it will ever draw is 13A!i am sure it ok and i havnt finished it yet the real long circuits which have a lot of sockets on i have ringed in 4mm volt drop is fine because what ever is plugged in can only draw 13A anyway and it will never ever pull 32A there really in no calculation to carrie out
4mm tw/e can take 32 A in trunking max volt drop would be about 10A on 70m circuit you can draw max of 13A for Ib
also onsite guide says max of 75m squared floor area
i do think its ok just on boarder but wont serve much
- - - Updated - - -
sorry not 10A --- 10V
i am sure it ok and i havnt finished it yet the real long circuits which have a lot of sockets on i have ringed in 4mm volt drop is fine because what ever is plugged in can only draw 13A anyway and it will never ever pull 32A there really in no calculation to carrie out
4mm tw/e can take 32 A in trunking max volt drop would be about 10A on 70m circuit you can draw max of 13A for Ib
also onsite guide says max of 75m squared floor area
i do think its ok just on boarder but wont serve much
- - - Updated - - -
sorry not 10A --- 10V
I get an Ib of 14.9A @ 70m, so presuming the load is spread along the length of the circuit, he'd get away with a 16A PD.
LOL....i am sure it ok and i havnt finished it yet the real long circuits which have a lot of sockets on i have ringed in 4mm volt drop is fine because what ever is plugged in can only draw 13A anyway and it will never ever pull 32A there really in no calculation to carrie out
4mm tw/e can take 32 A in trunking max volt drop would be about 10A on 70m circuit you can draw max of 13A for Ib
also onsite guide says max of 75m squared floor area
i do think its ok just on boarder but wont serve much
- - - Updated - - -
sorry not 10A --- 10V