If you put 32A load over 70M on the TLC online volt drop calculator, it tells you that you need live conductors of 10mm2
 
I have put a 4mm radial with about 20 sockets over 70 m the volt drop is 11 ma/m so at max of 13a the volt drop is about 10 V now I have a new question do I take the volt drop from 32 A or what I would say is 13A because I socket will only let you draw 13A

If anyone want to correct me then do it but not like a little boy
 
I have put a 4mm radial with about 20 sockets over 70 m the volt drop is 11 ma/m so at max of 13a the volt drop is about 10 V now I have a new question do I take the volt drop from 32 A or what I would say is 13A because I socket will only let you draw 13A

If anyone want to correct me then do it but not like a little boy

20 x 13 = ?
 
yes...it has to be max let through of OPD....not how many points it serves..
if it can let through a max of 32A...thats the figure you go with...
 
Have to be honest, 18 years experience, this is kids play, college stuff, I understand you want to ask questions about things, but you should already know basic stuff like volt drop, ccc and disconnection times
 