wannabesparky

ive been asked to fit 2 x 500w outside floods without p.i.r's inside a garage to replace the flourescents he has so that he can see better as he has some sort of disability.
I know it is assumed that a lighting circuit has 10 points and each to 100w which totals 1000w max.
But would 2 x 500w be ok? the garage has its own consumer unit etc.
Any help or advice would be greatly recieved. Thanks
 
2 500w floods will pull 4.2 amp so thats fine just mind they are not pointing at anything likley to catch fire after al l500w is a lot of heat close up.
 