Basically:
buried cable less than 50mm deep:-
within safe zone:30mA
within safe zone WITH earthed metallic protection (SWA, earthed conduit - NOT capping) - no RCd required (for cables)
Outside safe zone: 30mA WITH earthed metallic protection
Outside safe zone: must be earthed metallic covering (not allowed without)
Of course, if the cables feed sockets of 20A of less for use by ordrinary persons, or bathroom electrics, or equipment outside equipotnetial zone: RCD 30mA
UNLESS specifically labelled socket (ie Freezer only)
surface mounted CABLES do not need RCD but of course the circuit they are supplying may do (as above, bathrooms etc)
Obviously this will pretty much 'bin' the 100mA protection against fire RCD for TT's as well!