Has anyone got the big green book on hand?? What's the maximum current carrying capacity for each of the cables mentioned above? Clipped direct.

I have a 63amp test rig suppl from three phase board which customer wants moving from directly next to board to 15m away. What size cable??


From board looks like they have 16'mm cable for each phase....
 
6mm is 41A. 10mm is 57A method C, 3 core cable, 3 phase.

edit: 16mm is 76A.
 