goldie

Hello all.
Would you say main protective gas bond would be okay to install within 600mm on entry to the building although the pipework branch is external by meter cupboard? There is about 2 metres of gas pipe outside including the first tee.

Also standard fire rated downlight to be fitted in bathroom (not ip rated) but will be positioned above 2.25 metres and my belief is they wont be affected by the damp atmosphere etc.
Thanks
 
Read 7671 and you'll find the answers to both!
 
I would say these are both acceptable but if anybody has any positive input on the situation and a point to say not acceptable then I would like to hear it and possible reasons why not.
Ta
 
I most certainly wont be coming to your place, a scab wouldnt go to such a lowly place.
We beat u end of.
Anyway whats apprentices view on the question?
i repeat...you still have to go to elland road.....then we`ll see whats what...
 
Hello all.
Would you say main protective gas bond would be okay to install within 600mm on entry to the building although the pipework branch is external by meter cupboard? There is about 2 metres of gas pipe outside including the first tee.

Also standard fire rated downlight to be fitted in bathroom (not ip rated) but will be positioned above 2.25 metres and my belief is they wont be affected by the damp atmosphere etc.
Thanks

Bond ideally within 600mm of entry to building BUT before 1st branch / T

Above 2.25m is outside zones so no need for IP rating. Personally I prefer IP rated in bathrooms in any event as I find some non-IP downlights can suffer cosmetically due to steam. Then customer blames you for fitting them!
 
I most certainly wont be coming to your place, a scab wouldnt go to such a lowly place.
We beat u end of.
Anyway whats apprentices view on the question?

I seem to remember you got a hiding in the corresponding fixture last year! Oh and it was definitely a penalty!
 