Hello all.
Would you say main protective gas bond would be okay to install within 600mm on entry to the building although the pipework branch is external by meter cupboard? There is about 2 metres of gas pipe outside including the first tee.

Also standard fire rated downlight to be fitted in bathroom (not ip rated) but will be positioned above 2.25 metres and my belief is they wont be affected by the damp atmosphere etc.
Thanks

Bond ideally within 600mm of entry to building BUT before 1st branch / T

Above 2.25m is outside zones so no need for IP rating. Personally I prefer IP rated in bathrooms in any event as I find some non-IP downlights can suffer cosmetically due to steam. Then customer blames you for fitting them!
Ok cheers Njg28, sometimes takes a while on here before some1 gets to the point. input appreciated.
 
I most certainly wont be coming to your place, a scab wouldnt go to such a lowly place.
We beat u end of.
Anyway whats apprentices view on the question?

I seem to remember you got a hiding in the corresponding fixture last year! Oh and it was definitely a penalty!
Or we could talk about the year before that or even leagur 1 times.
Orrr when we won the league 3 times in a row back in 1920s.
Is this electricians forum?
 
Or we could talk about the year before that or even leagur 1 times.
Orrr when we won the league 3 times in a row back in 1920s.
Is this electricians forum?
they wont do owt wont town...

anyway....as i said earlier....within 600mm ideally.....its not cast in stone...

downlights OK if outside the zones....but i tend to look at stuff like is the showerhead fixed...or handheld?...if handheld then i ignore zones and go for IP regardless...

fire rated if theres a dwelling..or bedroom above.....
 
Goldie, I witnessed your first game this season and can honestly say they are the most negative team I have seen us play for a long time
 
That we will play each other at least twice this season, you needed me to explain that to you?
 
D No no I know that.
I mean we are all in the same crap league Like watching crap football so we arent Different other than fans like to annoy each Other
 
D No no I know that.
I mean we are all in the same crap league Like watching crap football so we arent Different other than fans like to annoy each Other

You watch a crap standar every week, but I know she I watch my team they generally don't play badly so you can only talk for yourself there
 
Haha how can you call them crap they are a Chanpionship team. I'm a Stockport fan, and we are crap! 5 relegations in 9 years!
 
Anyway, football aside, and you both support crap teams anyway, back to the thread. If you are outside the zones fit what you want, and bonding the gas wherever you want/can is better than not bonding it at all.

The regs are guidance, and must be complied under the banner of "Reasonably Practical", and this is why the EIC has a box titled DEPARTURES FROM BS7671. In both instances you need to apply common sense. Will the lights get wet/corrode etc, so consider the external influences and fit as appropriate. The gas must be bonded, so bond it wherever is convenient, and easily accessible.

Cheers…………….Howard

And if we get promoted again, we will do both of you next season. If you ever get to Wembley again, i can draw you a map of how to get there, i went twice last season. :-)
 
Last edited by a moderator:

OFFICIAL SPONSORS

Back
Top