If your existing oven is under 3kw with diversity applied you can put it on an existing ring & use the 6mm on the hob job done ,, seen loadsa ovens wired direct when theirs no need
 
If your existing oven is under 3kw with diversity applied you can put it on an existing ring
Not sure that's wise.

3kW with diversity is 4.4kW without so you would be putting a 4.4kW oven on a 13A plug.

The recommendation is that fixed loads of over 2kW should be on a dedicated circuit.

seen loadsa ovens wired direct when theirs no need
Not sure what that means.

There is a need to connect loads appropriately.


A 32A cooker circuit will happily cope with up to 15kW as in the vast majority of installations.
 
apply diversity to 3kw , most single ovens are 2.7 & the grill wont operate in conjunction with the oven in most cases so say 1kw grill / rest oven then apply diversity . ps loadsa = many
 
Ah, I now see what you meant but it wasn't what you wrote.

Punctuation would have helped.
 