Hi

Why is this? I swap a 4 pin round light for a double strip light ( working dead yes.) I have a two way consumer unit. this light circuit was on,what you call it?, the first RCD as well has a socket circuit.
I disconnected the round light and then the RCD kept tripping every few minutes or so.
The only thing I can think of, is that the single cable IS fed through a metal conduit and because I was touching the live, natural and earth, I may have been passing induced voltage to earth?

How wrong am I?
 
if you are working on a circuit with the MCB off, then you short N to E, the RCD will trip. that's as near as i can get making sense of your post.
 
Hi

Why is this? I swap a 4 pin round light for a double strip light ( working dead yes.) I have a two way consumer unit. this light circuit was on,what you call it?, the first RCD as well has a socket circuit.
I disconnected the round light and then the RCD kept tripping every few minutes or so.
The only thing I can think of, is that the single cable IS fed through a metal conduit and because I was touching the live, natural and earth, I may have been passing induced voltage to earth?

How wrong am I?
no...neutral current...hence Tel at #2
 
Last post does not make sense! Cheers telectrix.
What did you mean Glenspark by no...neutral current...hence Tel at #2
 