Just received a couple of Electrical Danger Notifications (C2's) from our annual electrical inspections.

"No co-ordination between conductor and protective device cct 1T/P 2.5mm - 32A ref method B"

&

"High values of measured EFLI at ccts 6TP-15TP"

Could you offer some advice as to what these mean, as I'd like to have some understanding before I talk to our electrical contractor.

Thank you in advance.
 
1 seems like an undersized earth conductor (cpc). it's a bit vague

2 is a high reading of the earth fault path on several circuits.
 
The person issuing the report should be explaining any issues so they are understood by the customer. Ask for clarification.

Issue 1 is saying that the cable used for the circuit is too small for the circuit breaker and vice versa. Simplest fix is to change the breaker size if the connected load will allow.

Issue 2 is saying the earth fault path of several circuits is not sufficient. Extra or larger earth conductors could be added or the size of circuit breakers reduced again if loads will allow.
 
Last edited:
The person issuing the report should be explaining any issues so they are understood by the customer. Ask for clarification.

Thank you for your reply Andy. I agree there should have been more information or at least some advice instead of just quoting the relevant regulation. I'll contact the inspection engineers and discuss with them.
 
Just received a couple of Electrical Danger Notifications (C2's) from our annual electrical inspections.

"No co-ordination between conductor and protective device cct 1T/P 2.5mm - 32A ref method B"

&

"High values of measured EFLI at ccts 6TP-15TP"

Could you offer some advice as to what these mean, as I'd like to have some understanding before I talk to our electrical contractor.

Thank you in advance.

Not quite sure in what context he is using coordination, there is no hyphen in the word. Not sure a 2.5mm cable and a 32 amp MCB can be classed as a "complex body but maybe as an activity"

Think it was an attempt of BS baffles brains
 
1- overload protectice device is too high for current carrying capacity of cable
2- efli is too high, you could reduce mcb size, upgrade cable size or install rcd 30mA on circuit which will give you max zs of 1667ohms.
 
1- overload protectice device is too high for current carrying capacity of cable
2- efli is too high, you could reduce mcb size, upgrade cable size or install rcd 30mA on circuit which will give you max zs of 1667ohms.

Thank you for you reply bigspark. With all the other replies, a little reading and having a good look at the circuits in question I've come to the same conclusion. Many thanks
 
If this is an ANNUAL report and the observations were not included in last years report there must be something remiss with any additions you have had done, or these observations have not been observed in the previous report.
If it is a breaker , or high efli on multiple circuits it is strange.

I must admit it is vague.
 
If this is an ANNUAL report and the observations were not included in last years report there must be something remiss with any additions you have had done, or these observations have not been observed in the previous report.
If it is a breaker , or high efli on multiple circuits it is strange.

I must admit it is vague.
The max Zs values are now lower than they were in previous years with the new amendment...
 
Not quite sure in what context he is using coordination, there is no hyphen in the word. Not sure a 2.5mm cable and a 32 amp MCB can be classed as a "complex body but maybe as an activity"

Think it was an attempt of BS baffles brains
It's how it's listed in the schedule of inspection now though isn't it.

Coordination of over current protective devices and cable size...or something along them lines...
 
If an RCD is already present in the system then it could be effecting the Zs readings. Had this multiple times and bypassing it or using the alternative Zs method proved it to be the RCD.

Obviously this depends on the current set up and if it is RCD protected or not.

One other thing regarding Zs values, If carrying out an EICR on an installation that was installed to say the 17th before any AMD's then if the circuits tested met these values then surely it complies to the edition/AMD it was installed to?
 
Last edited:

Reply to A little help please. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
675
This isn't really an electrical issue as such but I know you guys are pretty tech savvy and familiar with all the latest and greatest...
Replies
13
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
Hello Over the last 2 weeks I have been doing some electrical work for the neighbour of my Daughter as they had been let down by 2 other...
Replies
16
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock