I must admit the X .4 method is the one I generally use. This does however, highlight the problem with applying diversity. there is no hard and fast rule and each situation must be evaluated on its own merit. I do think the OSG formula is oversimplified and and can be misleading, at the end of the day it's the experience of the electrician that provides any accuracy in applying diversity.
 
Niceic assessors tell you to add up the total Number of amps and multiply by 0.4. Job done.
 
Why would you not use the OSG to apply diversity, when it is a book produced from the IEE wiring regs, the same institution that we all take guidance from ????

The ONLY formula that works for diversity/max demand in BS7671 or the on site guide, is the formula for Cookers up to 15KW. The rest are literary a waste of print on paper space, they don't and have never worked!!!

The standard formula that anyone with experience will use for max' demand, is that given by Malcolm...
 
You don't need to worry about an assessment, if they given you an ounce of grief mention how you've been thinking of going with one of the other scheme providers. You should then feel the tickle of a tongue somewhere up and around your prostate area.
 
I thought that with those scam providers, you pay up front to join, then they come and look at jobs etc..ask you a few questions, then if they aint happy, they charge you another couple of hundred quid, for another visit !!! Before they sign you up. Not that i want to worry you.
 
There's often similar innuendo in my posts but not many have spotted it mate, when I saw that I couldn't resist.

She asked me for a double entedre, so I gave her one
 
Long been converted to the 0.4 calculation from the likes of Malcolm.

I rarely work outside of domestic these days, but thought generally this rule was

0.4 Domestic
0.6 Commercial
0.8 Industrial
 