Hello all,
I will be getting assessed very, very soon now! I’ve completed the consumer unit change and am just having a bit of a panic as I’ve worked out the maximum demand and it exceeds the supply fuse by quite a bit.
I realise the assessor is not likely to questions my figures so I could write anything in max demand on the Electrical Installation Certificate but I’d rather bring his attention to it so he can see that I am capable of working out max demand properly and questioning the safety of something rather than trying to hide it.
Here are my figures, in case i have got something wrong:
1. Cooker (2.5Kw). 2500/230 = 10.9A. Apply diversity 30% of 0.9 = 0.27. First 10A + 0.27 = 10.27(plus 5A for socket attached) = 15.27A
2. Shower (9.5Kw). 41.3A (but on a 40A mcb) = 40A (No diversity)
3. Ring 32A (No diversity)
4. Shed (max demand approx 16.4A but on a 16A mcb) Apply diversity 40% of 16A = 6.4A (in reality I use about 3-4A at any one time!!)
5. Water heater 3A (combi) (unsure of any diversity, but wouldn’t help much))
6. lights (900w). 900/230 = 3.9A Apply diversity 66% = 2.6A
7. loft lights (200w) after diversity = 0.6A
Total Maximum demand = 99.87
The supply fuse is 60A on 16mm tails as are all the other houses around here, which all have the same things in them.
The DNO chap was out recently to fit an isolator and he said there were no signs over overheating or deterioration. It is still safe as 16mm tails protected by 60A fuse.
Have I worked out my diversity correctly?
No time to change tails/supply fuse as the assessor is coming too soon.
Any suggestions greatly received!!
I will be getting assessed very, very soon now! I’ve completed the consumer unit change and am just having a bit of a panic as I’ve worked out the maximum demand and it exceeds the supply fuse by quite a bit.
I realise the assessor is not likely to questions my figures so I could write anything in max demand on the Electrical Installation Certificate but I’d rather bring his attention to it so he can see that I am capable of working out max demand properly and questioning the safety of something rather than trying to hide it.
Here are my figures, in case i have got something wrong:
1. Cooker (2.5Kw). 2500/230 = 10.9A. Apply diversity 30% of 0.9 = 0.27. First 10A + 0.27 = 10.27(plus 5A for socket attached) = 15.27A
2. Shower (9.5Kw). 41.3A (but on a 40A mcb) = 40A (No diversity)
3. Ring 32A (No diversity)
4. Shed (max demand approx 16.4A but on a 16A mcb) Apply diversity 40% of 16A = 6.4A (in reality I use about 3-4A at any one time!!)
5. Water heater 3A (combi) (unsure of any diversity, but wouldn’t help much))
6. lights (900w). 900/230 = 3.9A Apply diversity 66% = 2.6A
7. loft lights (200w) after diversity = 0.6A
Total Maximum demand = 99.87
The supply fuse is 60A on 16mm tails as are all the other houses around here, which all have the same things in them.
The DNO chap was out recently to fit an isolator and he said there were no signs over overheating or deterioration. It is still safe as 16mm tails protected by 60A fuse.
Have I worked out my diversity correctly?
No time to change tails/supply fuse as the assessor is coming too soon.
Any suggestions greatly received!!