When I was doing the ACA exam mock test I have been looking at this question and think it’s wrong? A final circuit supplying a 2 kW boiling water tap is wired using 2.5mm2 PVC insulated
copper conductors with a 1.5mm2 circuit protective conductor, and is 15 m long. The
installation has a Ze of 0.65 ohms. Taking in to account the maximum permissible operating
temperature of 70° C with a correction value of 1.2. What will be the value of the measured
Zs for this circuit?
a) 0.87 Ω
b) 0.91 Ω
c) 0.94 Ω
d) 1.16 Ω
Resistance Value R1+R2 is 19.51x15/1000 = 0.292 so add this to Ze and it is 0.292+0.65 = 0.94. Which they say is the right answer but where is the correction factor. Should that not be 0.94x0.8= 0.75.
Please help can’t get my head round it.