Discuss Adiabatic Equation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
DYCHE4230
Hi All,
Can anybody help....Trying to establish if I would have to change the mec on a TNS system....
Ok So S=sqr(I2xt)/k
When establishing the value of 't' do I use the characteristics of the distibutors main fuse or the main switch in the CU or I have missed the point entirely?:rolleyes:
And when establishing 'I' do I use 230v or 240v
Some direction in this matter would be most helpful.
Thanks in advance.
i think you have to use the value of the main fuse.
use 240v, that is still currently the UK energy providers output voltage, and is likely to be for a long time as they are making more money out of us this way :(
Why are you trying to calculate the size of mec when you should be using table 54.7 in relation to meter tails[largest size conductor].
Hi, I don't want to change the existing MEC if I don't have too. So was gonna check if the existing is adequate if not then I'll upgrade them as table 54.7
Thanks for your quick replies....
Reply to Adiabatic Equation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the...
4K
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Hi wondering if you could help with some advice Been running an Essex/suffolk based electrical firm for last 20 years, mainly light commercial...
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...