ezzzekiel

utilising an old cooker circuit to power new external building, and for some reason calc gave me cpc of 4mm which i duly ran in. on checking later im now getting 6mm from a diff calculator at home.

type c 32a
no regs at hand for zs so:
32x10 = 320
Zs = 230/320 = 0.71ohms

fault current 230/0.71 = 323a

s= rootsq 323x323 x 5/115 = 6mm
 
Disconnection times aren't guessed chaps, you determine them from the time/current graphs in ol'red using the fault current.

As you've used the max Zs of 0.71 (worst case scenario and shouldn't be anywhere near this) in this instance for the calc, the fault current happens to put the dis time at 5s, nothing to do with it being a distribution circuit or other.
 
Last edited by a moderator:
Lenny is right, also i would go further and say if you are going to calculate the protective conductor size you need all the facts, you can't just guess Zs.

Therefor you use table 54.7 so 6mm earth it is.
 
you can't just guess Zs.


type c operation at 10 x In
so 32a type c would equal (32 x 10) 320a
230v / 320 a = Zs 0.718 (0.72ohms)

max Zs for type C from brb = 0.72ohms

not a guess at all just calculated.
 
No it's a guess. You can't calculate Zs without knowing Ze and the length of cable to calculate R1+R2.

You've quoted max Zs as in the regs. You should be less than .8 of that anyway which gives 0.576 have you calculated that?

Also the Zs could be .1 or 1.5 or anything.

That's why you use table 54.7 in this situation.
 
you misunderstand the calc is based on max figures and i was talking about calculating max zs!

ive calculated using maximum alllowed figures because i have no other figures to work with so its not a guess at all for the calculation im doing.

I understand what you are saying though
 
Last edited by a moderator:
No it's a guess. You can't calculate Zs without knowing Ze and the length of cable to calculate R1+R2.

You've quoted max Zs as in the regs. You should be less than .8 of that anyway which gives 0.576 have you calculated that?

Also the Zs could be .1 or 1.5 or anything.

That's why you use table 54.7 in this situation.

If you use the full calculation for working out Zs you can use the tables the 0.8 is useed as a rule of thumb when when testing and not using all the correction factors Ct,Cg,Ci ect.
 